WHAT IS THE USAGE OF Buckoltz relay IN POWER TRANSFORMER AND
AND HOW ITS FUNCTIONS?
Answers were Sorted based on User's Feedback
Answer / wasif
in case of fault enormous amout of heat is generated in the
main tank which decompose the oil as a result of which
gases are produced. When the gases travel from main tank to
conservator tank they causes the float of buchholz relay to
be inverted which in result makes the tripping contacts and
thus causes the breaker to be tripped.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nagaraja bagi
Buchholz relay is used for Transformer Internal faults,bcoz
of over load or internal faults more heat will produce it
decomposes the oil and produces the gas and because of
transformer insulation gas will produce and it will try
move from main tank to conservator bcoz it is light in
weight then alarm float will operate and gives the alarm if
it exceeds then tripping float will operate and trip the
Breaker of Transformer.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / anant shetye
In power Transformer Gases form so before putting
Transformer in service we have to release that gases & LET
OIL SHOULD come to conservater tank for safe operation ,if
it is not do so and if you give supply to the transformer
Buckoltz relay gets trip & it provide safety to Transformer.
Is This Answer Correct ? | 2 Yes | 1 No |
8. A DYNAMOMETER TYPE WATTMETER RESPONDS TO THE.......
In protection core of a C.T. why Knee pont voltage is greater than SLV and in metering its viceversa?
what is the contact resistance of Air circuit breaker??
WHY PROTECTION CT IS USED NEXT TO METERING CT?
why induction motors are rated at 0.8 power factor.
For a three phase induction motor, what will be the effect on motor if the neutral of the system is shifted to say 20 deg.?
State the methods of improving power factor?
What is short circuit analysis of electrical networks?What are the procedures to be followed for its calculation?
how many wires need to be bring to the motor if its star delta starter
at high temperature conductivity increases for conductor what will happen for long transmission when temperature is high?
do you have some of interview Questions in power and genrator section in general whith answers
say a transformer is designed for 33/11kv step down with ratio 0.33 for load 1 mva. if am giving 11kv as a input that same transformer what will happen to its o/p voltage. and whether it can be operated for 500kva