FOR ELECTRICAL TRANSMISSION TOWER WHAT SHOULD BE THE MINIMUM
HEIGHT FROM THE GROUND? AND WHAT SHOULD BE THE DISTANCE
BETWEEN THE TWO CONDUCTOR?
Answer / k.prakashchandra
For extra high tension tr lines, the minimum clearance is
not less than 5.2 mtr+ 0.3 mtr for every 33 Kv or part
thereof by which the voltage of the line exceedes 33
Kv,provided that the minimum clearance along or across the
road shall not be less than 6.1 mtr.Clearances between
conductors for 66 Kv 75 cm,110 Kv- 125 cm ,132-160cm,220-
210 cm and 400Kv-410 cm
| Is This Answer Correct ? | 5 Yes | 2 No |
List advantges of active filter over passive filter?
To have variable speeds we use a. Induction motor b. Traction motor c. Shunt motor
which meter used to measure a flus
How to calculate 33 kv panther conductor line losses.
1 Answers Construction, Orange,
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
synchronous motor of 13.5MW having which type protection? and how to set relay?give me relay setting calculation for different protection for this motor assume efficiency,power factor and other term if neccecery
why occ characteristics of generator is also called as magnatization characteristics
What is the advantage of Neutral graunding transformer insted of Neutral graunding Resistance in generating station explain briefly.
In Delta connected capcitor bank, One bank failed due to some problem. Can we connect Open delta capacitor bank to 3 phase motor. The motor voltage rating is 6.6KV. IF yes what changes will happen?
How to select Main CB Rating for 187 KW Load?
Is there any problem if i connect APFC panel in generator circuit
At 765Kv, I have seen the use of PT at line side for metering and CVT for protection, although as far as my knowledge is concern, PT at this voltage level will have huge loss and more cost as compared to CVT as CVT can also perform same function of Protection and Metering? So my question is why use PT and not CVT for metering and protection in order to reduce the cost.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)