we r having 3 core 3 1/2, 4 core cables how we can know
this cable has to be used for this purpose?
Answers were Sorted based on User's Feedback
Answer / kh
3 core is used for 3-ph loads/systems which do not require
neutral e.g. motors. 3.5/4 core is used wherever 1-ph
supply is also required (tapped between 1ph-N) in addition
to 3 phase supply. 4 core used for smaller cables usually
upto 16 sqmm where neutral core is of same size as phase
cores while 3.5 core is used for higher sizes where neutral
core is half the size of phase cores.
Is This Answer Correct ? | 24 Yes | 0 No |
Answer / at
3 core cables are used where ever the system is ungrounded.
3.5 core cables are used where the major load in an
industry / plant etc. is three phase but also has single
phase loads or loads that can cause a little unbalancing
and thus the nutral might carry some current but not always
and not as much as the line current. Therefore a smaller
cross section of nutral can solve the purpose as current
through nutral will be very small as compared to the rated
current of the cable.
4 core cables are used in systems where all loads are
single phase or majority loads are single phase. so there
are chances of high degree of unbalancing. and nutral has
to carry a larger amount of current.Therefore half cross
section of nutral may not solve the purpose and we opt for
4 core cables. This arrangement is used for small cross
section cables used in homes and industries. for lighting
and other small applications.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / pawan mishra
3.5 core cables contain 4 cores i.e. 3 for phase and 1 for
neutral.
it is known as 3.5 coz it s netral thickness is half the
diameter of phase core.
netral is requried only in l.t. network
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / p.k.chadhar
3 core cable can be used for three phase power supply
without earthing
3&1/2 cable can be used for three phase power supply with
earthing because 1/2 core is mostly used for earthing or
gounding
4 core cable can also be used for three phase power supply
with earthing this cable can also be used for control supply
it depends on size of the cable if it is 1.5 mmsq.then
control ,if size is more can be used for power connection.
Is This Answer Correct ? | 2 Yes | 10 No |
Answer / ashok
4 core cables are used for the rating more than 5KW,and the
3 core ,31/2 are used for below 5kw and 5kw supply.
Is This Answer Correct ? | 3 Yes | 24 No |
Why we apply 100ADC for contact resistance measurement?.If we apply AC what will happen
A single line diagram(SLD) and a purchase order of a 11/66kV switchyard of a power plant was given. In the SLD, only one lightning arrestor(LA) was shown, but the purchase order had need of 3 LAs. Is this correct, if yes, why?
MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III
What will happen if the voltage in my house drops from 220V to any lower voltage?
what is the mean of"turbo" in turbo alternator???
What is High Frequency Grounding????
why do MCB melt but not tripped in lighting highmast??
Technical specification of a wind farm
How to calculate the heat load for a electrical room
how to calculate transformer load?
We have AC-transformer 110/13.8kv,40MVA.If DC-Voltage=110kv is applied in its primary what will happen?
how do u calculate CT rating for 10 mva transformer