How the Oil Surge Relay works? How it protect the OLTC?
Answers were Sorted based on User's Feedback
Answer / n. manohara rao
THE OIL SURGE RELAY IS CONNECTED IN BETWEEN OLTC CHAMBER AND CONSERVATOR (SEPARATE FOR FOR OLTC) WITH BREATHER. A SEPAATION SHOULD BE ARRANGE SUCH THAT THE OIL IN OLTC CHAMBER AND TRANSFORMER CHAMBER SHOULD NOT BE MIXED TOGETHER. IN CASE ANY ON LOAD TAPCHANGER A PROBLEMS DEVELOPED DURING OPERATION A GAS IS DEVELOPED AND THAT GAS WILL ACTUTE THE OIL SURGE RELAY AND AND THE RELAY ACTIVATES OTHER CIRCUITS AND MAIN CIRCUIT HT WILL BE OPNED WITH ALARAM INDICATION AND FLAG INDICATION
| Is This Answer Correct ? | 59 Yes | 17 No |
Answer / satish raman pathak
It is a gas operated relay.It is placed between Main Tank & Conservator Tank,with an angle5-7 Degree.There are2 Mercury switches, one in the top & other in the bottom of Bucholz relay,filled with Transformer Oil. When small amount of vapour passes through the relay Top Float will operate, gives Bucholz alarm.In case of heavy internal fault, Large amount of Bubbles forms,operates the Bottom Float , Gives Bucholz Trip.In case of Bucholz Alarm/Trip Relay contact to checked first(IN Alarm/Trip Relay contact will change).then if there was any gas formation occured.Gas should be relaesed through the top Vent of relay( in that time hissing sound is observed in case of Gas present).Have to release all other top vent in Main Tank & Radiator Top.
In case of OLTC, there are saperare OLTC Surge Relay, same as Main tank Bucholz Relay.
After gas release if Trafo again tripped in Bucholz.Then there must be some hot spot/heavy internal fault in Trafo.other necessory testing to be carried out, like Ratio test,Magnetic Balance test,Vector group test,IR Test for further fault finding.
| Is This Answer Correct ? | 3 Yes | 10 No |
Answer / subrahmanyam
We have faced the issue of Oil surge relay during rain. The
raly operated due to which complete plant tripped. First
GCB openeed and First out is turbine so tripped on turbine.
| Is This Answer Correct ? | 9 Yes | 17 No |
respetsed sir, i have applied for section engg and juniour engg for both chennai and tiruvunabthapur boards for electrical deportments . can u suggest what books i have to follow and and also from which sections they r going ask (i mean weightage and what topics i have to cover) for both se and je for both chennai and tiruvunanthapur boards.......
why return path in terms of neutral is required please give a relevant answer
purpose of breaker contact multiplication relay?
For high voltage and low current Circuit Breaker preferred is vacuum circuit breaker.why?
what would the resistance of a 110v 150w submersiblepump motor windings be
using in R,Y& B PHASE LTSIDE(415V)ct ratio 4000/5 WITH ENERGYMETR OF 1280 REV./KWH,240V.WHAT WILL BE MF OF METRE.
what composit error,ratio error,phase error in CT and PT??
what is neutral grounding resistor?
how the direction relay sense rhe directional fault?it's forward or reverse?
what is feeder?
What is the distance between each insulator in 33kv transformer and how can it calculate
I have suguna 3 hp pump for my agreeculture work.It deliver the water from 45 feet well .I suffered by powercut.During powercut i got 2phase supply only .My question is can i run the pump in 2 phase supply using capacitor?.Can u explain me how to connect the capacitors?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)