CAN 50Hz transformer work at 60 Hz power supply? if yes how
it is possible?
Answers were Sorted based on User's Feedback
Answer / sathiarajan
Yes it can. But it will get more heat, Bcos of hystersis &
Eddy current loss. The Core, winding impedance, etc have
been calculated for 50Hz. If it is increased to 60Hz then
impedance of the transformer will also increase. It can
work with 60Hz under light load for a very short duration.
Is This Answer Correct ? | 14 Yes | 2 No |
Answer / raghvendra kumar
Yes it is possible at 60 Hz also and it will work same as at
50 Hz but losses i.e. Eddy current loss is directly
propotional to square of frequency and hysteresis loss is
directly proporional to frequency (generally), so if we put
it on 60 Hz then more constant loss will occur which reduces
the efficiency as well as rating (due to Thermal limit).
Is This Answer Correct ? | 13 Yes | 1 No |
in 3 phase induction motor resistance value is how much
how vector surge relay works ?
What is master trip relay? How does it work?
hai every bodi please let me know the test procedure for lightning arresters.
In which working principal temperature transmitter work.explain in detailed.
back emf of motor at the time of starting ?
what is solkor relay and which condition it will act?
how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
what are ABCD curves in MCBs and how we observe that curves?
How can we calculate C10 rating of a bttery from c5 or c20 ratings??
when we use neutral line as grounding.
What is principal to reduce earth leakage current with isolation transformer? When isolation transformer is installed in input stage of system, earth leakage current is reduced. the reason is why the leakage current of 2nd stage of isolation transformer does not affect the 1st stage's leakage current. I would like to know the reason. As you know, earth leakage current is a kind of AC. So, How to reduce earth leakage current in case that isolation transformer is used?