why is the rating of transformer done in kva and not in kw.
Answers were Sorted based on User's Feedback
Answer / manthesh.patil
transformer is rated in kva bcoz cu losses are dependent on
current and iron losses are dependent on voltage ,& they are
independent on powerfactor so transformer is rated in kva
not in kw
| Is This Answer Correct ? | 39 Yes | 5 No |
Answer / lakshmanan m
According to my opinion, manufacturer cant design the
particular transformer for specific load (capacitive or
inductive load) Thats why they dont give the power in KW.
Because KW= vxIx power factor. but power factor is
depending upon the load. So commonly they are give the KVA
power only. It means KVA= Vx I only. According to the load
we can calculate the KW rating.
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / manoj-essar
dear manoj, there is no concern of static or rotating
device, then why r u saying in this way?
Trafo is not having unity pf but it depends upon load type
of trafo...(inductive or capacitive or resistive load)
| Is This Answer Correct ? | 17 Yes | 6 No |
Answer / sachin /vaibhav
as core loss depends upon voltage & copper loss on
current independant of PF. HENCE RATING IS IN KVA
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / vasumalai madhavan
In transfomer, the core loss depends upon voltage and
copperloss depends on current , it was (transoformer) not
dependable on power factor . thats why the rating of the
transformer always in kva not in kw....
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / shinyvikram ganji
rating of the transformer is done based on losses(core and
copper losses).
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / ravi
transformer losses are in terms of current and voltage only
i.e (I Square R) copper loss and VI is the Core loss. i.e y
units are in KVA
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / beau
because transformer capacity takes care of both real power
consumed by resistive loads and reactive power in inductive
and capacitive loads such as motors and the transformer's
windings inductive reactance(Apparent power KVA).
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / thiyagarajan
kv is an apparent power kw is an active power the ratio
between active and apparent power is power factor ,we dont
know the power factor before connecting to load that why we
are used to refer kv in transmission
| Is This Answer Correct ? | 1 Yes | 0 No |
What is differential relay? How it operates?
Can run 11KV(5MW) slip ring motor by appling 415V? if Yes and what are the processors?
what is current
how to make parrallal ups
all interview questions with answers of ntpc (2000-2009
What is the name of oil which is used in transformer?
what are the duties of commutator in motor and generator?
is earthing is necessary if we use armoured cable
1 Answers ABB, Schwing Stetter, Siemens,
what is the formula to find out how many amps generater takes running on full load.
which is the most common harmonics 3rd,5th,7th affect the systegm
If we need4× 50mm sq cable but it's not available so we can pull 4×25mm sq 2cables
what is the working of ups.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)