why is the rating of transformer done in kva and not in kw.

Answers were Sorted based on User's Feedback



why is the rating of transformer done in kva and not in kw...

Answer / giridha

because the core losses and cu losses depends on only
voltage and current and is independent of power factor so
t/f rating is in KVA

Is This Answer Correct ?    50 Yes 8 No

why is the rating of transformer done in kva and not in kw...

Answer / manthesh.patil

transformer is rated in kva bcoz cu losses are dependent on
current and iron losses are dependent on voltage ,& they are
independent on powerfactor so transformer is rated in kva
not in kw

Is This Answer Correct ?    39 Yes 5 No

why is the rating of transformer done in kva and not in kw...

Answer / lakshmanan m

According to my opinion, manufacturer cant design the
particular transformer for specific load (capacitive or
inductive load) Thats why they dont give the power in KW.
Because KW= vxIx power factor. but power factor is
depending upon the load. So commonly they are give the KVA
power only. It means KVA= Vx I only. According to the load
we can calculate the KW rating.

Is This Answer Correct ?    18 Yes 0 No

why is the rating of transformer done in kva and not in kw...

Answer / manoj-essar

dear manoj, there is no concern of static or rotating
device, then why r u saying in this way?

Trafo is not having unity pf but it depends upon load type
of trafo...(inductive or capacitive or resistive load)

Is This Answer Correct ?    17 Yes 6 No

why is the rating of transformer done in kva and not in kw...

Answer / sachin /vaibhav

as core loss depends upon voltage & copper loss on
current independant of PF. HENCE RATING IS IN KVA

Is This Answer Correct ?    11 Yes 3 No

why is the rating of transformer done in kva and not in kw...

Answer / vasumalai madhavan

In transfomer, the core loss depends upon voltage and
copperloss depends on current , it was (transoformer) not
dependable on power factor . thats why the rating of the
transformer always in kva not in kw....

Is This Answer Correct ?    6 Yes 2 No

why is the rating of transformer done in kva and not in kw...

Answer / shinyvikram ganji

rating of the transformer is done based on losses(core and
copper losses).

Is This Answer Correct ?    4 Yes 2 No

why is the rating of transformer done in kva and not in kw...

Answer / ravi

transformer losses are in terms of current and voltage only
i.e (I Square R) copper loss and VI is the Core loss. i.e y
units are in KVA

Is This Answer Correct ?    3 Yes 1 No

why is the rating of transformer done in kva and not in kw...

Answer / beau

because transformer capacity takes care of both real power
consumed by resistive loads and reactive power in inductive
and capacitive loads such as motors and the transformer's
windings inductive reactance(Apparent power KVA).

Is This Answer Correct ?    4 Yes 2 No

why is the rating of transformer done in kva and not in kw...

Answer / thiyagarajan

kv is an apparent power kw is an active power the ratio
between active and apparent power is power factor ,we dont
know the power factor before connecting to load that why we
are used to refer kv in transmission

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Generally we denote power in 'p',voltage in 'v'but why can't we denote current in 'c' instead of I.

4 Answers   Bhel,


How can you start-up the 40w tube lite with 230v AC/DC without using any choke/Coil?

2 Answers  


What is called grain-oriented laminations?

0 Answers  


What is the basic difference of turn ratio & transformation ratio for a transformer?

8 Answers   IGT,


What is difference between earth leakage relay and restricted earth fault relay ?

22 Answers  






what maximum range of star & delta in hp or kw ?

0 Answers   Makkah Hilton Towers,


How to calculate cable size in sq units based on motor rating is KW

2 Answers  


in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel ?

2 Answers  


how to use single phase supply for a three phase equipement.

12 Answers  


What is the deference between earth fault & earth leakage

1 Answers  


How would your past experience translate into success in this job?

0 Answers  


what are the basic insulation levels & what its Unit

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)