What is the formula to calculate the rating of a thermal
over load relay
Answers were Sorted based on User's Feedback
Answer / barkha jha
At starting motor draws current 5 to 6 times of the flc so
overload relay setting is done this kept on mind.for e.g
3.7 kw motor the
FLC is 8 amps. we can select the relay 6A-10A range.
tripping setting is 90 % of FLC
Is This Answer Correct ? | 38 Yes | 7 No |
Answer / jayakumar.k
There is no General formula .but the general practice is
motor FLC should be the setting . for e.g 3.7 kw motor the
FLC is 8 amps. we can select the relay 6A-10A range. 8Amps
shoud be the trip setting.
Is This Answer Correct ? | 25 Yes | 17 No |