We have one Energy meter for Measuring the
voltage,current,power,energy(KWH,KVARH,KVAH) & power
factor.The problem is that the meter does not show whether
the PF is lagging or leading.So i want to know that is
there any way or calculation to find out that whether the
PF sign (lagging or leading) depending upon the above
mentioned parameters?
Answers were Sorted based on User's Feedback
Answer / john
Is this a revenue meter from the utility company or a power
quality meter? In the case of a power quality meter, there
should be something letting you know if your PF is in a lead
or lagging. I have an Amprobe DMII Pro and it showes an i
after the PF to indicate lagging, .98i, and a c to indicate
leading, .98c. I have also seen meters with lagging PF -0.98
and leading +0.98. Another simple thing you can do is look
at your VAR, if it is in the negative, your in a lead.
As far as a revenue meter from the utility company is
concerned, call the utility company and ask them.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ram
please check the meter must be indicating sign as +
(leading) or - (Lagging) power factor.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / ds01151
By using the formula KW/KVA you can find the pf
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / ashwini
by using formula p=vicos(pf) v can calculate power factor......
| Is This Answer Correct ? | 1 Yes | 9 No |
starting torque is increased and current is decreased by using external resistance in a slip ring induction motor. How??
is it necessary to earth the rmu before cutting off the transformer winding?if yes why?
What is the name of transformer oil?
how to enter inverter parameter? without manaual?
What is load staggering or load shifting in the context of power distribution?
What should be the length of transmission line so that we can see/obtain the full sine wave of voltage??
What is mimimum di -electric strength value for 33 KV transformer OLTC oil
how to match 0 -10V with 4 - 20mA
in shunt clippers why a resistor is used in sereis with the input
how netral CT is selected (including its details specification)
8 Answers ABB, ABC, dbpl, Mecon, Shree Engineering, Tapasya Transformers,
Briefing the effects of ASR and ACR of a double closed-loop speed regulating system.
Pls tell me whether we can use EN3A material for shafts of Permanent magnet alternator.What will be the effect of magnetic and nonmagnetic material for shafts on magnetic properties of PM rotor .
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)