what is OLTC and difference between RTCC and OLTC
Answers were Sorted based on User's Feedback
Answer / sathishbabu t
oltc-onload tapchanger
rtcc-remote tapchanging circuit
rtcc connected to oltc to control the voltage onload
Is This Answer Correct ? | 32 Yes | 1 No |
Answer / sanjay
OLTC is the onload Tap Changer & it vary
the taps of the transformer in auto
according to the utility power to ensure
safe range of power is been fed to the
connected load.
RTCC is the remote tap changer circuit & it
is related to the OLTC. The taps can be
changed in manual too from RTCC. Also, no.
of alarm & the connected Tap position can
be viewed through RTCC.
Is This Answer Correct ? | 16 Yes | 1 No |
oltc means on load tap changer
and rtcc remote tapchanger control circuit,
rtcc use for operating oltc from contol desk of equipment
rtcc is a control circuit for oltc and oltc used for voltage
control.
Is This Answer Correct ? | 14 Yes | 0 No |
Answer / rakesh sharma
OLTC means on load tap changer & RTCC means remote tap changing control.OLTC change the tap according to voltage variation & oltc get signal from rtcc, according to voltage variation it increase or decrease the tap.RTCC get signal from HT panel.If HT voltage high or low RTCC give signal to OLTC to increase or decrease the voltage.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / asim
RTCC "Remote Tap Changer Control" which is programmable device to control the output of the transformer through OLTC "Over Load Tap Changer" unit fitted in the transformer and connected to RTCC through control cable.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / naresh reddy
dear friend
r t c c means remote tap changer cubical
o l t c means over load trip coil
Is This Answer Correct ? | 1 Yes | 38 No |
While performing stability test of differintial cts how to know the voltage and current on both side of the transformer?
Write down the name of 2 lady Bir Pratin of Bangladesh
what is divercity factor?
how to select a cap,when a fan is required 2.5 micro ferad cap,then how we know about 1 hp motor?
Hi, I'm running plastic reprocessing company where all motors are running only in delta. Due to that when I use start my 30 hp motor my transformer gets fuse. Where it happens two times a day. I gt a suggestion from a person about Automatic Power Factor Controller APFC. Is it useful for my problem??? Or is der any other way for solving this problem?? Upgrading the transformer is difficult. Pls give Me ur suggestion. Waiting for ur reply.
2 Answers Shree Lingaa Polymer,
why ferranti efect occurs on no load only?
Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR) Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
Why do we perform an open-circuit test and short-circuit test on the transformer?
if v r considering a 4000/1A ct,if v inject 1 amps in secondary core wat happens?(consider as 2 core ct,each for metering and protection)
how to calculate energy meter multipling factor by ct & pt raitio
can a rotating machine give the DC output without commutator? if yes, how? if no, why?
working method of railway electricl loco in single wire 25000 volt