Should transformer earthing pit, to be connect to earthing
mat in Substation
Answers were Sorted based on User's Feedback
Answer / niranjan
ยท The system earthing and safety earthing are interconnected and therefore fault current flowing through system ground raises the potential of the safety ground and also causes steep potential gradient in and around the Substation. But separating the two earthing systems have disadvantages like higher short circuit current, low current flows through relays and long distance to be covered to separate the two earths. After weighing the merits and demerits in each case, the common practice of common and solid (direct) grounding system designed for effective earthing and safe potential gradients is being adopted.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / siva kumar
during fault conditions the fault current fed from transformer neutral.So the earth pit which is connected to neutral has to supply fault current.
supplying of quantity of fault current by earth pit has limitations such as soil type.CIPipe lengh etc.
if you connect neutral earth pit to substation mat, the mat will supply the fault current.
it is just like earth as big water reservoir and water as current. If more and more parlel pipe lines are laid more quantity of water can be dischrged quickly.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pankaj agarwal
as the short circuit fault devlops in the system the fault
current flows from fault point into the neutral. in the
absense of interconnection, all the fault current has to
travel through ground which have high resistivity so the EF
current flowing in the system may not be sufficient to
operate the EF trip relay. in the interconnected system EF
current have alternate and less resistive path so fault
gets cleared fast.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nipesh
but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), in this case transformer body earthing and substation earthing both are joint through metal gland, is this safe for transformer and other equipment?
| Is This Answer Correct ? | 1 Yes | 0 No |
If single phase voltage level is 230V than why three phase voltage level is not 660V ?, but it is only 440V.
16 Answers BSNL, DOS, EFS, HMT, L&T, TCS, ThyssenKrupp,
How many electrones need to flow in one second to equivalent to one Ampere.
why substation rating interms of 11 multiples???like 11kv/33kv iis there any special reason???
I AM COMPLETED DIPLOMA IN E.E.E. AS WELL AS B.TECH IN ANDHARPRADESH.. HOW I THE Certificate of competency as Electrical Supervisor.
How can i modify the design of 3 phase induction motor to be as 3 phase synchronous motor??
If a 3 phase transformer is a 500 kva using the formulae 500kva= 500000/433 x 1.732 = 666.71amps does this mean that each phase on the secondary side is 666.71
Three phase star connected PT transformer primary side one phase fuse is blown what will be the output in secondary side(Secondary side also three phase star connected)
What Is Connection APFC Panel In Compony.
whether a separate starter is used for a motor while it is connected to a vvvf panel?
im electrical engineer, could any one help me for FEWA exam questions please ?
If I want to use capacitor banks at HT (11 KV) side for maintaining power factor then which type of capacitor should I use? Plz give me the specification?? (I am using 1250 Kva transformer (11 KV/433V)).
What is burden of ct,explain very simple
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)