Answer / k.prakashchandra
The VA per phase is (500/3 KVA) 166.67 x 1000 , phase
voltage is(433/1.732) 250 V.Then current in each phase is
166670/250= 666.68 A
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / shyam
The value 666.71 A gives the current rating i.e the maximum
current that the transformer secondary winding (each phase)
can withstand.The operating value may be less than or equal
to this RATING...
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / lalit pratap
Yes It's caring 666.71amps on each phase on secondary winding in transformer.
| Is This Answer Correct ? | 0 Yes | 2 No |
How many Zones can be in Conventional type fire alarm system & how can we detect the fire in Conv. type FAS?
what is armature reaction?explain in simple words?and what is its infleunce on dc motor
What's an AVR? What's its purpose in Generators?
Is phase preventer require when overload relay is there
how can i change the rotation of the AC single phase induction motor and show me by diagram
Is there any reason that a vertical motor can not be mounted horizontally ? I happen to have one and would like to use it horizontally to save money by not buying a new horizontal motor.
what is the difference between fc-tcr and tsc in facts
3 Answers SCET Shadan College Of Engineering and Technology,
Explain different types of d.c motors? Give their applications
my N-P 230 VAC at 3 wires but i haven't any voltages at phase to phase whither my supply is 3 phase, why i haven't received these line to line voltages ?
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
advantage of motor design on higher power factor . normally motors are designed for .8 power factor. what is advantage of designing at .88 power factor
what are pilot cells
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)