Answer / k.prakashchandra
The VA per phase is (500/3 KVA) 166.67 x 1000 , phase
voltage is(433/1.732) 250 V.Then current in each phase is
166670/250= 666.68 A
Is This Answer Correct ? | 8 Yes | 4 No |
Answer / shyam
The value 666.71 A gives the current rating i.e the maximum
current that the transformer secondary winding (each phase)
can withstand.The operating value may be less than or equal
to this RATING...
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / lalit pratap
Yes It's caring 666.71amps on each phase on secondary winding in transformer.
Is This Answer Correct ? | 0 Yes | 2 No |
What is difference between miniture circuit breaker and module case circuit breaker up to 63Amp.
how we can calculate cable size of 230v,1 hp single phase motor ? panel to motor distance is 25 meter
what is the difference betweem star connected motor & delta connected motor?
What is marx circuit?
How does a diesel generator works?
1.what is mean by 8/20 micro sec waveshape
how the percentage impedance affect the transformer loading when connected in parallel.?
what is ht breaker
where we use zero sequence current transformer or core balancing ct.
how braking & making capacity of circuit breaker are calculated?
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
explain harmonics in simple words..........