What is the correct procedure to shutdown VCB in 11kv substation.safety and work procedure..

Answer / query

The correct procedure to Shut down VCB is to first trip the
VCB through Manual/electrical command . Then open the
Downstream(outgoing) isolator earth it for any trapped
charges. repaeat the same with the Upstream(Incoming)isolator.

Is This Answer Correct ?    14 Yes 2 No

What is the correct procedure to shutdown VCB in 11kv substation.safety and work procedure..

Answer / balaji

1. Preparation (Permit to work)
2. Separation (Trip the Breaker)
3. Isolation (Isolator isolates)
4. Earthing & Short circuit (Earthing)
5. Screening & Marking the area (Barricading the work area)

Is This Answer Correct ?    11 Yes 2 No

What is the correct procedure to shutdown VCB in 11kv substation.safety and work procedure..

Answer / manzoor hussain

1)First need to obtain isolation permit(work permit)
2)Confirm substation no., breaker no.
3)Inform to control engineer
4)Transfer the load from LV side
5)First need to trip the vcb(electrically or manually)
6)Disconnect DS switch (isolator)
7)Need to close the earth switch (ES)

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example?

2 Answers  


How to Calculate Current Rating of SDFU (Switch Disconnector Fuse unit) for Protectionof Capacitor Bank connected to Busbar of 800Amp,in LV side of 11/0.433KV, 250KVA Transformer?

0 Answers  


Are same transformer be employed for step up and step down services?

3 Answers  


explain safety measures in alternator?

0 Answers  


A 30KW motor running at 1450 rpm draws 56A, how would you determine if this is correct or not?

3 Answers  






A long transmission line is limited by - a)thermal limited b)voltage limited c)stability limited d) L,C limited please explain with proper reason.

1 Answers  


why single induction motor is not self starter?

3 Answers  


What is difference is of VSD,VFD,VSDS, are they the same as the direct current to control dc using above mention

0 Answers  


how dc load convert to ac load

3 Answers   Sunpower Solutions,


How many types of Transformers are there?

8 Answers  


what is servo motor and how it works?

0 Answers   Godrej,


how we calculate electricity unit ( meter unit.. for knowing how many charges) from on motor load.?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)