Can a transformer designed for a particular voltage and
frequency rating be used for different set of mentioned
ratings? Assume that the winding does not get burnt because
of overheating at higher voltage.
If yes, then under which constraint it is possible?
Answer / iamdon
Yes.
A transformer designed for a particular voltage and
frequency rating can be used for different set of
mentioned ratings as long as ratio of voltage to the
frequency does not deviates from designed value.
By emposing this constraint, the core of the transformer
will not saturate.Since the winding is assumed capable of
sustaining overheat, so only deciding factor is V/f ratio.
i.e,(V/f)=fixed at rated value.
50 Hz at 500V
25 Hz at 250V
75 Hz at 750V and so on.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 8 Yes | 0 No |
what is dc system? how getting pulse from rectifier?
Can we inject more current in ct primary paralleling 2 loading transformers/Injection kit at a time?let ct ratio be (5000/1A)(per kit rating 2000A range),i need to inject 5000A,if this cant b done means wat is d optional?
how instantanious short circuit current is calculated ? its formula.
what is earth resistance? how to measured? and give values at power station and mcc area?
For load of 1 nos 3 TR Air Conditioners,6nos of 60 Watt Tibe Lights, 2 nos 200 W Outdoor Lights,1 no Coffee maker.All may work at the same timehow do I select DG Set Rating ,pLease advise the calculations
What is SFU why it is used
how to calculate the change over time for star delta starter for different KW motor?
HOW TO BUILD THE SINGLE PHASE TO THREE PHASE CONVERTER? CAN PROVIDE ME CIRCUIT..THANKS
What is the latest generation of circuit breakers called?
Why Utility Distribution System in India is mainly at 11 kV? Why not Utility go for 33 kV?
how to find value of resistance when 1 kw consumption for 10 minutes
is 60hz freq better than 50 hz?&why?