what is vector surge & vector shift? we have 25.3 MW(11kv)
generator & 11kv/132kv transformer, connected with with 132
kv grid.vector surge relay is tripping frequentaly.what is
permissible maximum limit for this.
Answers were Sorted based on User's Feedback
Answer / gobind
Whan the generator have synchronized with grid the waveform
have 120 Deg each phase but at the time of any fault
occurred in the grid system,at that time the waveform of the
grid voltage have been reduced from 120 Deg to min at that
time vector Shift Relay have operated.Permissible limit of
the vector Shift 8 Deg.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / ajay vikson
Hi,
here is a useful link on the vector surge relay
http://www.electrotechnik.net/2009/04/vector-surge-relay.html
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.p.sharma
We have the vector surge relay setting at 12 deg. But i observe that at that setting many time tg breaker tripped with grid breaker as per scheme only grid breaker trip is required. Please tell me is this setting ok or not.
K.P.Sharma
| Is This Answer Correct ? | 0 Yes | 0 No |
Why infinite busbar has zero resistance and high mechanical inertia?
what r the main parts of central chiller plant in Air conditioner ? explain the function of each?
What is the safety factor is to be consider while selecting the switchgear and protection for electrical system
what happen if power factor goss to above unity (one) ? of any electrical system or motor.
I have a 5KVA UPS. Total load to be connected almost 3KW. Ordering a battery pack with capacity of 1920VAh. How long will the backup time be?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating
What is purpose of APFC panel?
7 Answers Techno Electric and Engineering,
how we calculate the short circuit capacity of the busbar in LV & HT?
In which connection the voltage will be more , in star or delta connected motor?
what will be the breaking capacity of MCCB of 1000kVA (6% Impedence) transformer? Voltage being 415V, Power Factor 0.8.
why a motor overheated stops to rotate ?????
Determine the MVA rating of the power transformer given that 110/66 kV,1000 Amps. Folks how can i calculate the MVA rating with this Data??Plz Help........
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)