Why restricted earth fault protection is needed? Why can’t
differential
Protection is sufficient?
Answers were Sorted based on User's Feedback
Answer / anaz.a
restricted earth fault protection is a protection scheme given in assistance to the differential protection.it is given to protect an earth fault which occurs very close to the neutral point in star connected windings of the transformer.this kind of fault a very low fault current only and this current may not be sufficient to activate the differential protection relays.
The sensitivity of the differential relays cannot be increased beyond a limit since this may lead to unnecessary tripping(the transformer may trip even for an earth fault occurring on the outgoing feeder Side)
Hence a special scheme of protection called REF(Restricted earth fault)is provided in order to protect a restricted area of the winding from internal earth fault.
Is This Answer Correct ? | 32 Yes | 1 No |
Answer / bandarawy
Due to the fact that current transformers always have a
certain error, the differential current always differs from
zero as soon as there is a load current flowing. Especially
during a through-fault condition with high short circuit
current , the differential current may be very high due to
the error of the current transformers. Depending on the
sensitivity of the setting value of the overcurrent
protection relay, when it is used as a simple differential
protection relay, unwanted tripping may occur.
For this reason, it is necessary to stabilize the
differential protection by means of a so called bias
current. For the restricted earth-fault protection using
the biased differential protection principle
Is This Answer Correct ? | 3 Yes | 8 No |
what are the analog quality input for protection function?what are minimum reqiments?
If cvt is most advance & effective(economically & stability)so why not use instead of VT(11 kv & 33 kv)?
what is the path of thunderlightening? once both a buffalo and a person were standing 5m apart but lightening hit and killed buffalo not person?
PLZ EXPLAIN THE INTERLOCKING AND CONTROLLING OF CONTACTORS????HOW CAN I DO THAT?
how does we calculate the capacity of battery
How calculate cable size & voltage drop for the following requirement connected load 150 KW distance cable length 1000 M voltage 3 phase 415 v.
In 11KV Double pole structure for each phase we are using Disc one Insulator. Why we are not using 2 r above insulators instead of one insulator?
for a 500 KVA connected load, I calculated 30% of capactor for power correction. Even after using 225 KVR capactor PF is not improving. What could be reason for low Phase correction factor?
Why do u join toreent power ?
What are the effects of electrical faults?
how to calculate the tarriff for an industry whose kva demand is 10 mva
how r charge carriers produced