Why restricted earth fault protection is needed? Why can’t
differential
Protection is sufficient?
Answers were Sorted based on User's Feedback
Answer / anaz.a
restricted earth fault protection is a protection scheme given in assistance to the differential protection.it is given to protect an earth fault which occurs very close to the neutral point in star connected windings of the transformer.this kind of fault a very low fault current only and this current may not be sufficient to activate the differential protection relays.
The sensitivity of the differential relays cannot be increased beyond a limit since this may lead to unnecessary tripping(the transformer may trip even for an earth fault occurring on the outgoing feeder Side)
Hence a special scheme of protection called REF(Restricted earth fault)is provided in order to protect a restricted area of the winding from internal earth fault.
| Is This Answer Correct ? | 32 Yes | 1 No |
Answer / bandarawy
Due to the fact that current transformers always have a
certain error, the differential current always differs from
zero as soon as there is a load current flowing. Especially
during a through-fault condition with high short circuit
current , the differential current may be very high due to
the error of the current transformers. Depending on the
sensitivity of the setting value of the overcurrent
protection relay, when it is used as a simple differential
protection relay, unwanted tripping may occur.
For this reason, it is necessary to stabilize the
differential protection by means of a so called bias
current. For the restricted earth-fault protection using
the biased differential protection principle
| Is This Answer Correct ? | 3 Yes | 8 No |
what is sevice settings for mccb?How can be it setted?
Where the ON LOAD TAP CHANGER is provided in the setp up transformer?
what is the resistance value of our human body?
What is the function of an Auto reclosure relay. How does it work??
Define pole pitch?
single phase can run in PVC conduit. Three phase can also run in one PVC conduit. But two phase cannot run in one PVC conduit. WHY? reply plz....awaiting your answer.
How to calculate the value of capacitance of a capacitor used in power factor improvement plant if we know KVAR and voltages?
which fault current is maximum: 3 phase short circuit, LG, LL or LLG?? why?? in one of the problems that i have solved, 3 phase short circuit current on an unloaded generator came out to be less than the LG fault current. can anybody please explain why.
How is the connection of the tap changer on the HV side been made?
difference between power surge and switching transient
how do i calc busbar size for a rated current?
What happen if 200KVAR capacitor continuesly connected to load and all the plant machinaries are not in working?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)