Classical power system stability was mainly focussed on
rotor angle stability but modern power system stability has
more focus on voltage stability.Why?
Answers were Sorted based on User's Feedback
Answer / iamdon
Majority of blackout/grid failure now a days is due to
voltage instability phenomenon.
This is because Modern power system is very vast and
interconnected to form a grid network.Also generation is
not sufficient to meet the load demand which is incresing
rapidly, due to which load end voltage drops.To maintain
load end voltage and power factor within permissible limits
shunt capacitors are used extesively at almost all load bus
bars(Over compensation),which has detrimental effect on
voltage stability.
At the time of peak load(load increase),the voltage at the
load end decreased so reactive power supplied by shunt
capacitors also reduced.So when we have most need of
reactive power supply,the shunt capacitor prove less
capable.
That's why modern power system satbility problem shifts
towards voltage stability.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / arvind
in todays time also rotor angle as well as voltage
stability anlaysis are been in focused, if rotor angle is
not into consideration then why so much transient analysis
is into picture.
Is This Answer Correct ? | 1 Yes | 0 No |
Yes...Arvind.
Your proposition is right.
I had just made a relative analysis with two stabilities
involved.It does not means that the rotor angle is of no
importance today.It just establish the fact that now we
MORE FOCUSSED towards volyage stability.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dharmesh
actualy both are cosider in today's power system the difference is rotor angle is for protection of generator and voltage regulation is for load regulation.
Is This Answer Correct ? | 1 Yes | 0 No |
Explen all type electrical protection ? like O/C,E/F,NPS,VOLTAGE UN BLANCE,CURRENT UN BALANCE,NAGETIVE PHASE SEQ,AND ETC...............electrical Protection
if the transformer at full load have a iron loss =900w and copper loss = 1600w . what percent of the load will the transformer has a maximum efficiency?
What is the equipment used to control the generator output?
what do you mean by leading power factor & lagging power factor
WHY EXCITER PHASE SEQUENCE ARE OPPOSITE THAN STATOR SUPPLY PHASE SEQUENCE IN SYNCHRONOUS MOTOR >
what is the effect come when i changed the alternator exciter field winding DC palority(+ve & -ve)which is coming from AVR.
Two bulbs of 500w and 200w rated at 250 v will have resistance ratio as ?
2 Answers CGL, Dreamz Infra, Sunny Developers,
In a company has been installed an analog amperemeter, this company was suplied by generator X, there is no problem in the ampere meter, rigth now this company's supplied by generator Y then the pointer in amperemeter vibrating. What happened? Why? Thank's
why the supply frequency in india is 50hz?
what will happen if we use earthing inplace of neutral for domestic energy meter
5 Answers Polyplex Corporation Limited,
1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason
16 Answers Ecil, Engineers India, MahaDiscom,
What is the function of wave trap in an electrical substation?