for a 11kv transmission line what capacity of CTs & PTs are
required?
Answers were Sorted based on User's Feedback
Answer / srinivasan.s
For 11KV line CT ratio was 1200A-600A-300A/1Amp
PT ratio was 11KV/110V
for 11KV CT's PT's minimum 3cores are available
generally 1'st core for metering
2nd and 3rd cores for protection purpose.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / khalid k usafzai
for installing cts and pts on 11 kv line first of all the load to be connected is required.then we will proceed.bye
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / shivadathathri
11 KV CTs & PTs , Out door Pedestal mounting versions will do. Current ratio , STC Rating & Insulation level can be determined with connected load. Like breaker / Transformer Etc. Example : Load is 11KV 100KVA transformer is connected . Then use 11KV Cts CTR: 5/5 Amps , Class 0.5 for metering , Class : 5p10 for Protection . OCF - 150XI nominal . Oil cooled CTs for MUSS. If it is mounted inside panel / Control room then Use Resin cast type. SHIVADATHATHRI- 9632153842.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / alternate_reality
A 100/5 Amp CTPT can be installed for metering purpose in
Indsustries...
Is This Answer Correct ? | 2 Yes | 3 No |
What is lifting power for 1 wb/m2 and 1 A magnet?
what is the function of closing coil in air circuit breaker?
What is oil temprature with A/T contacts in Transformer ?
In vapour absorption refrigeration machine fluids used are
In CDG type IDMTL realy O/L , E/F, O/C which are used for out going feedrs,on R-phase o/c element, Y-phase , e/f elecment and on b -phase o/c element will be connected . Why the earth fault on center phase only, why not on other two phases?
i want to syncronise 5 nos of DG. How? pls reply
what is the RMU and RMU system in sub-station(11kv,66kv.....)
2 Answers Alstom, Torrent Power,
HOW TO WORK A VFD?SAY SIMPLE METHOD
how to calculate neutral current in three phase four wire system
Less cost of delta connection over star connection a. No fourth neautral wire
What type of wiring series or parallel is used for conventional and addressable type FAS & why?
what is purpose of using reactor in substations