Why CT secondary should not left open??????????
Answers were Sorted based on User's Feedback
Answer / iamdon
The CT secondary should not be left opened secondary due to
following reasons:
1)Zero current in secondary leads zero back emf.So primary
current becomes very high.Large heat generated may burn the
winding and core.If the transformer sustain this heat, even
then its operation becomes improper as explained below.
2)CT is bascially a step up transformer.So high voltage
induced in secondary may saturate the core (core becomes
permanently damaged).So the operating point advances in non
linear region,which makes the transformer operation improper
(secomdary current will not replicate the primary according
to the turn ratio).
3)High voltage induced in secondary side may endanger the
life of personnel working on the side.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 16 Yes | 2 No |
Answer / bhautik patel
due to the absence of the counter ampere-turns of the secondary, the unopposed primary mmf will set up high flux in the core which will produce excessive core loss with subsequent heating & high voltage across the secondary terminals.
Is This Answer Correct ? | 3 Yes | 0 No |
diesel generator not getting start so whats problems will happen to DG and how we can start DG
what is meant by the phrase 'static load' in case of shorting in a generator excitation system?
how to calculate units consumption for a 12 hp motor /hr.
1) What is difference b/w impedence relay and differential relay? 2) what are substations equipments? 3) what is difference b/w circuit breaker and isolator? 4)what are the types of circuit breakers? 5) which medium is mostlty used in circuit breakers and why it is used?
How can we calculate the rating of capacitor bank to be connected for a particular load(ex.100kw)to improve the power factor from 0.8 to 0.9?
How much ph is maintained of water electrolyte which is used in LRS for 1200 kw slipring induction motor ?
0 Answers AMS, JK Lakshmi Cement,
Which power will flow first if we switch on a motor Active or Reactive? How?
I want Primary side delta and Sec side Star connection transformer . but i have received Star - Star transformer ,shall i use the same transformer by giving the only 3 ph on Primary side without Neutral connection on the Starpoint.
WE HAVE THE DC RECTIFIER 1500A, INPUT VOLTAGE IS 3 PHASE. HOW TO CALICULATE THE LOAD? 3 PHASE SIDE EITHER dC SIDE. PLEASE SUGGEST ME
diameter of cable and core is doubled then the value of capacitance is
Why HT motor is connected in Star?
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?