Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Y to use 4 to 20ma instead of 0-10v

Answers were Sorted based on User's Feedback



Y to use 4 to 20ma instead of 0-10v..

Answer / ravinder

Because Voltage drops as resistance of cable conductor
increases but current will be same at any point of the
loop.4mA is called Live Zero,shows liveliness of the loop
when process variable is zero.

Is This Answer Correct ?    27 Yes 4 No

Y to use 4 to 20ma instead of 0-10v..

Answer / jaldeep

For signal transmission we are using 4 to 20 mA, because of
following reasons.
1. If you are using 0 to 10 for long distance then
signal will be dropped due to cable resistance you will not
get correct feedback
2. 4 to 20 mA will give correct feedback even for
long distance. It will not drop according to cable
resistance. Only you have to keep loop impedance as per
your field instrument.
3. Open loop, you can easily detect in 4 to 20 mA.
You can program if mA is less than 4 then you can define it
as open loop.
4. For 0 to 10 v input if cable is open then it will
be difficult to identify that cable is open or input is 0
volt.

Is This Answer Correct ?    17 Yes 0 No

Y to use 4 to 20ma instead of 0-10v..

Answer / himanshu

beacause total loop resistence is 250ohms.
so 24VDC supplied loop 1v corresponds to 4mA
and 5v corresponds to 20mA.
HART PC communicates to 1-5VDC only.
As explained in above answer 4mA is LIVE ZERo.
for 20mA reason is above 20mA current can be hazareous for
fieled.(fire).like HC and Refineries
thats why 20mA signal is used.

Is This Answer Correct ?    9 Yes 4 No

Y to use 4 to 20ma instead of 0-10v..

Answer / ecxlsync

current signal is used because as explained
it will not change even the loop resistance is changed
due to transmission lines resistance. it is stated in the KCL that current entering in the circuit will be equal to the
current leaving no matter if the circuit resistance is changed.

Voltage signal is greatly affected by the circuit resistance.
long distance transmission has large wire resistance that
will cause large voltage drop.

Is This Answer Correct ?    1 Yes 0 No

Y to use 4 to 20ma instead of 0-10v..

Answer / kalpesh

Because if we use 0-10V signal and if there is a break in
cable loop then it will show 0V which is the low level of
the measured signal but in reality it is a signal failure
from transmitter.

Is This Answer Correct ?    4 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , so what to do for solve this problem. The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?

0 Answers   QAFCO,


Can anybody tell me the exact explanation for Functional calibration?When it should be done on process or on lab? Advanced Thanks

2 Answers  


What is the constant voltage unit?

0 Answers  


How to calibrate the pressure Transmitters

1 Answers  


what type problems create in radar level transmeter and what is its solution

2 Answers   Essar,


what is the advantage of submersible level transmitter compare to ultrasonic level transmitter?

0 Answers  


wht is Zero Elevation and Zero Suppression?

12 Answers  


how does we do bench calibration of a differential transmitter.

1 Answers  


why micro controller 8051/52's clock frequency is internally divide by 12 ?? and why it is further divide by 32 in UART serial communication ??

1 Answers  


how to calculate orifice sizing? and tell me if pipe size bet 50mm t0 200mm then we can use pipe flange??? and above 250mm pipe size should i use D & D/2 Flange? is it right or wrong?

0 Answers  


What is the purpose of LO Overhead tank in turbines.

0 Answers   ADMA OPCO,


I faced several time siemens ps2 positioner automatically getting Chang in it's set point direction after auto calibration  So is there any causes biside this or  any  permissives ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)