How to find knee point voltage in current transformer?
Answers were Sorted based on User's Feedback
Answer / yogesh
10 % increase in voltage gives you 50 % increase in
excitation current is called knee point voltage.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / pundlik wanwe
for getting knee pint voltage of CT following is the procedure.
voltage source is connected to the CT secondary and slowly voltage is increased. milli ampere current is measured in the secondary circuit. at initial increase in current will be linear with voltage which is operating range. if again the voltage is increased further, at some point 10% increase in voltage causes 50% increased in current. this point is called Knee point of CT. Knee point is very important for the protection CT as after this point CT core is on the verge of saturation, which is not healthy region for protection.
Is This Answer Correct ? | 0 Yes | 0 No |
What are conduct on the testing in cf in ur site?
In AC Drives How can change & control its output Frequency?
What is Partial Discharge test .Please specify that this test can be test on 11/0.433 KV,630 KVA Transformer.
If load current is 70amps or 50amps what range of CT to install for ampere metering
what is the diffrantial relay???????why we use it on the MDB
can i connect REF and Differencial relay in 1 CT core for transformer protection?
how to interlock 3 nos MCCBs using under voltage coil. please provide me circuit diagram?
Explain why machinery used on a.c supply is usually rated in KVA instead of KW?
i have some screw comprressor with 630kw power,i have established them with simple star to delta circuit,by the way there is so much inertia when the screw comprressors start, can you offer me contactors power with 400vac or any cataluge to choose the contactors
send me the upsc conventional papers of 2006
1 Answers Juniper Networks, Siemens,
1sq mm dc powr cable can carry how much dc currnt
What happened when a three phase induction motor work on two phase supply.9