i have one absolute pressure transmitter for the range is
-400mmhg to 400mmhg. If i do the zero trim at atmosphere the
transmitter should be give 4ma or 12ma? which one is correct?
Answers were Sorted based on User's Feedback
Answer / banerjeenandan
Your transmitter has a range of 800mmhg. The LRV is -400mmhg
and URV is +400mmhg. So at atmosphere you will get 12mA. all
the time, because atmosphere is Zero gauge pressure
(perfectly mid value in between the LRV and URV).
If you do zero trim at atmosphere, it will take "ZERO" with
the atmospheric pressure. The range of the transmitter will
not change. The range will remain 800mmhg. But your LRV will
change to 0mmhg and URV will change to +800mmhg. So in that
case, without any process connection it will give 4mA.
Is This Answer Correct ? | 25 Yes | 1 No |
Answer / senthil.doosan
-400mmhg= -0.53bar
400mmhg = +0.53bar
if u do zero trim by opening the valves with respect to atm
the output of the transmitter is 12ma
without any process connection the output is 4ma
Is This Answer Correct ? | 7 Yes | 0 No |
What is instrumentation control?
What is the loop calibration? Which instrument used to loop calibration and how?
what is plc?
27 Answers HPCL, KRL, Noor Company, Petrochemicals, SS Automation,
what is different between 2,3&4 wire rtd and how much maximum distance using plc to field.
WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HIS message appears: Equalize start. HIS0163 WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. HIS0163 ---- ERROR = 3 WARNING = 1 ---- Tell me, please, why and how to solve the problem."
6 Answers Khas Pvt Ltd, Yokogawa,
HOW CAN I CONNECT ROSEMOUNT 3300 LEVEL TRANSMITTER TO Allen-Bradley SLC500
hello dear i have faced problem in drum level transmitter. the problem is when i engrize the meter meter shows 100% but the actual level 40 or something plz suggest me
In my plant I want to mount a steam flow transmitter .Flow nozzel is already mounted in steam line .So how can i know the range to put in flow transmitter?
Why ac supply load cell is used? Can we use the dc supply load cell?
Why we are using DPT(Differential Pressure Transmitter) in separator instead of level trasmitter?
Explain the difference between plc and cnc?
what is vibration a part of proceess variable? if vibration is a part variables then how we minimize the actual vibration on machine on load,? vision of instrumentation contrl plz ans me IPGDL interview question