What is the technical name of Transformer Oil ?
Answers were Sorted based on User's Feedback
Answer / arvind singh
There is not any technical name for the transformer oil,
its only the specification which made the crude oil to
transformer oil(insulating oil). Nepthanic oil, Peraphenic
oil, Mineral Oil (its the specification which process the
crude oil to the nepthane base for the cooling of
transformer which have various acceptance norms as
specified in IS:335 below
Sl No. Characteristics Requirement Method of test as
per latest revision of IS as indicated below
1. Appearance The oil shall be clear and
transparent and free from suspended matters/sediments A
representative sample of oil shall be examined in a 100 mm
thick layer at the ambient temperature
2. Density at 29.5 Deg. C. Max. 0.89 g/cm3
IS:1448[P:16]
3.
Kinematic Viscosity at 27oC Max. 27 cst
IS:1448[P:25]
4. Interfacial tension at 27oC Min. 0.04 N/m
IS:6104
5. Flash point Pensky Marten (closed),Min.
140oC IS:1448[P:21]
6. Pour point Max. -6 deg. C IS:1448[P:10]
7. Neutralisation value (Total acidity) Max.
0.03 mg KOH/G IS:1448 [P:2]
8. Corrosive Sulphur Non-corrosive IS:335
9. Electric Strength (breakdown voltage)
IS:6792
a) New unfiltered oil, Min. 30 kV (rms)
b) After filtration, Min. 60 kV (rms)
10. Dielectric dissipation factor (Tan delta) at 90ยบ C,
max. 0.002 IS:6262
11. Specific resistance (resistivity)
IS:6103
a) at 90oC min. 150x1012 ohm-cm *
b) at 27oC min. 2500x1012 ohm-cm *
12. Oxidation stability IS:335
a) Neutralisation value after oxidation Max.
0.40 mg KOH/g
b) Total sludge value after oxidation Max.
0.10 percent by weight.
13. Presence of oxidation inhibitor present by weight
The oil shall not contain anti-oxidant additives
IS:13631
14. Water content maximum 50 ppm IS:13567
15. Aging characteristics after accelerated ageing
(open beaker method with copper catalyst)
IS:12177
Method A
a) Specific resistance (resistivity) Min.
IS:6103
1) at 27oC, Min. 4.5x1012 ohm-cm
2) at 90oC, Min. 0.2x1012 ohm-cm
b)Dielectric dissipation factor (Tan delta) at 90oC
Max.
0.20 IS:6262
c) Total acidity, Max. 0.05 mg KOH/gm IS:1448
[P:2]
d) Total sludge, Max. 0.05 percent by weight
Annex A of IS 12177
16. SK value, max. 4-8% volume increase IS : 335
Is This Answer Correct ? | 40 Yes | 10 No |
Answer / gokulakrishnan
Transformer oil, or insulating oil, is usually a highly-
refined mineral oil that has excellent electrical insulating properties.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / nage
No such name but can you tell me what IP/ASTM/any other
thermometer is used to maintain 27 deg C of KV bath?
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a k singh
Poly Chlorinated Biphenyl (PCB) or Askerials.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sanjeev
TRANSFORMER OIL NAME
TECHINICAL NAME IS CRUDE OIL' BUT
ACCORDING TO BOSS LUBRICANT' CANADA
THE CHEMICAL NAME OF THIS OIL IS
SEVERELY HYDROTREATED HEAVY NAPHTHNIC DISTILLATE(SHHNH)......
..;;;;;;;;;;;;;
:-)
Is This Answer Correct ? | 4 Yes | 5 No |
What is real time power factor control panel(RTPFC)?
1.wat is the advantage of induction motor? 2.wat is diffrence between 1-phase and 3-phase induction motor?
How npn and pnp transistor works
If a motor of 8.5 KW with same load and using in both Star & Delta one by one,then which will take more current in star connected or in delta connected
What is Automatic interlocking circuit dighram between two contactor for DG SET panel.
Slip at maximum torque depends on A rotor resistance and reactance B stator reactance C load current D stator resistance
For household Load of 11Kw supplying 5Nos. 1.5 ton Air conditioners + usual other load what shall be rating of Either ELCB Or ELMCB? Which of the circuit breaker will be a better choice?
what is tri state logic gate
if we want to increase the back up time of an UPS what should we do ? if we want to decrease the charging time of a battery/batteries attached with the UPS what should we do ?
What is the most important precaution in any experiment with d.c. Shunt motor?
What is the function of Igniter in 250 watt HPMV street light?
What is the need of earthing transformer for delta side of a transformer. (Think of a line section between a star/delta transformer at a grid substation and delta/star transformer at a village. An earthing transformer is there at the delta side of the star/delta transformer at grid substation). As there are no ground reference there will not be fault current if a one phase is grounded. Further L-L phase will be sensed by the primary side of star/delta transformer as a L-G fault. So why an earthing transformer is required at delta side