Why CT secondary should not be kept open?

Answers were Sorted based on User's Feedback



Why CT secondary should not be kept open?..

Answer / ashok bhatnagar

CTs are used for the measurement of high currents as a
primary sensor. The output of the CT is normally connected
to the relevant ammeter which has very low impendence and
secondary remains almost short circuited. The secondary
current has no control over primary current in a CT. If
secondary is open circuited two things will happen :
1. Due to absence of secondary current no counter magnetic
field is produced and flux in core of CT rises to
saturation level which can change the charateristics of CT
and damage it permanently
2. since number of turns in secondary is very high (1:
1000) for , a very high voltage may be induced in secondary
that can harm the prsons working on the instruments panel.

Is This Answer Correct ?    308 Yes 27 No

Why CT secondary should not be kept open?..

Answer / arvind chalka

if secondary is open then secondary current and flux will be zero. so that total flux is increased.
emf is directly proportional to flux than there will be induced a high voltage that saturate the core and demage the transformer.........thus we should not be open secondary .

Is This Answer Correct ?    89 Yes 9 No

Why CT secondary should not be kept open?..

Answer / achint rajput

A current transformer should never be open-circuited while
main current is passing through the primary winding. If the
load is removed from the secondary winding while the main
circuit current is flowing, most of the primary winding
current becomes magnetizing current, but the vector angles
change in such a way as to keep the total current in the
primary the same as before. Because the main circuit is now
mostly magnetizing current, the flux in the core shoots up
to a high level and a very high voltage appears across the
secondary. Due to the high turn ratio usually found in these
transformers, the voltage in this condition can reach a
dangerously high level, which can break down the insulation.
It also becomes a hazard to personnel. The high flux can
saturate the core and result in strong residual magnetism
left in the core, thereby increasing magnetization current
and introducing error in the transformation ratio. One has
to put a short on the secondary winding before removing the
connections.

Is This Answer Correct ?    27 Yes 5 No

Why CT secondary should not be kept open?..

Answer / iamdon

The CT secondary should not be left opened secondary due to
following reasons:

1)Zero current in secondary leads zero back emf.So primary
current becomes very high as the primary resistance is very
low.Large heat generated may burn the winding and core.If
the transformer sustain this heat, even then its operation
becomes improper as explained below.

2)CT is bascially a step up transformer.So high voltage
induced in secondary may saturate the core (core becomes
permanently damaged).So the operating point advances in non
linear region,which makes the transformer operation improper
(secomdary current will not replicate the primary according
to the turn ratio).

3)High voltage spikes(order of kV) produced in secondary side
may endanger the life of personnel working on the secondary
side.

4)High voltage spikes(order of kV) produced in secondary side
is sufficient to break down the transformer insulation.

Author:arbelectbit@yahoo.com

Is This Answer Correct ?    30 Yes 19 No

Why CT secondary should not be kept open?..

Answer / rites

CTs are used for in the measurement of current as a primary
sensor. The output of the CT is connected to the relevant
power meter. For CT the primary is the busbar / cable
caarying current which generates current in the secondary
by induction. Now if CT secondary is kept open and current
flows through primary the induced emf in the secondary will
not have a close path to flow which will lead to opening /
bursting of the CT.

Is This Answer Correct ?    38 Yes 29 No

Why CT secondary should not be kept open?..

Answer / seema

If we kept the secondary of current transformer open, current in the secondary side will be zero, voltage get increased so it will worked as a VT. At the primary side current is maximum so maximum flux will get inducced in the primary side & zero in the secondary side.so, in that case the difference between the primary flux & secondary flux will be more so the counter balance between that 2 flux is impossible.Result will be increased in primary current, increased in core losses.

Is This Answer Correct ?    6 Yes 6 No

Why CT secondary should not be kept open?..

Answer / pillay

In the physical construction of CTs you can see the secondary
is made up of a winding but the secondary is just one cable or
busbar.So it acts as a step up transtrofmer when the secondary
is left open.It is real I have seen two people who have had their hands burnt due to careless handling of the CTs.

Is This Answer Correct ?    12 Yes 33 No

Post New Answer

More Electrical Engineering Interview Questions

The Q-facr o of a coil given as wL/R. what will be shape of Q versus frequency graph.

0 Answers   GATE,


what is meant by dielectirc medium? what is the dielectirc value of air and water???

2 Answers   ISRO,


What type of surgery impedence with 200ohs 

1 Answers  


why ct ratio always rated 5.

1 Answers  


What is defference between earthed and unearthed cable(HT)? Which is better for under ground cabling?

1 Answers  






Phase control and integral control are used for?

0 Answers   NPCIL,


We operate a 10 Mw facility and we have been experiencing several trips due to fluctuations on the MVAR? We have checked all issues related to the AVR and we have found all OK? Can anyone help us? The grid voltage, internal voltage, all regular parameters look ok. MVAR fluctuate and there it goes the unit? What could be happening? Thanks!

5 Answers  


what is the use of compensation in designing a transmission line

1 Answers   Genco,


what is the difference between thermal magnetic release and microprocessor based release breakers. what are the advantages of latter over the first one...

5 Answers   Jackson, Karthik Industries, McD BERL, TCS,


Why Transistors are not used as switching devices?

15 Answers  


for 4 MVA , 33K.V/6.6K.V transformer. secondary side the connected load is 3000H.P. What is the rating of capacitor bank to be insttaled.

0 Answers   SCCL,


What kind of battries are generaly used with Disel Generator?

1 Answers   Exide,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)