Why star point of star connected motor is not grounded?
Why alternator is operated at lagging power factor?
Answers were Sorted based on User's Feedback
Answer / leo felix.d
The transfromer's secondary which is feeding 3 phase motor
is already earthed.so there is no need to earthe the motors
star point again. Because earth resistance wont be same
every where.If we eartherd both the ends,there will be a
current flow between two neutrals.
universaly,in industries 70% of loads are inductive tupr
which are having lagging PF nature.Always load only decides
the power factor not source(Alternator).So that only the
rating always mentioned as VA and not watts.
Is This Answer Correct ? | 30 Yes | 5 No |
Answer / avinash
3 phase star connected motor no need to grouned neutral
because mostly load current is balanced. But 6.6 KV y
connected motor has provided neutral c.t. for protection
purpose. so grounded neutral is providing in HT MOTOR.
Is This Answer Correct ? | 3 Yes | 7 No |
Answer / santosh kawade
3 phase motor is a balance load, hence we are not require
to connect star point of star connected motor to ground.
Due to balance load there will not be any current flow from
neutral and connecting star point create unnecessary
wastage of material and money.
santosh kawade
Is This Answer Correct ? | 3 Yes | 17 No |
How two nos. 130 kw D.C motor get synchronise using D.C drive.
What will happen if the voltage in my house drops from 220V to any lower voltage?
why ct ,cvt should be stored in a vertical position?
what will be the motor terminal box connection arrangement (star or delta). on what basis it decided?
What is the universal motor?
what is the right cable size for 100 hp mpter.
what are inductive and capacitive voltage transformers.what are their applications
Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract engg that due to return current coming in neutral & impropper earthing this happend. But after all set up & load balance we checked & found again we have about 20 to 32 amp return current on neutral. we have 12 airconditioner + 12 mini fridge on single phase line. Pl suggest any idea to solved this problem
Hello friends, Can anyone explain the concept of zones in Bus bar protection and how can we differentiate the main zone and check zone in Bus bar protection
What are the basic properties of signal flow graph?
I am going to appear for the RRB Chennai Section Engineer online exam. Please send me the question papers from 2001 to date to my mail id:upendrakrishna20@gmail.com,plz send me ,or send any other rrb papers plzzzzzzzzzzzzzzzzzz
draw the full wave and half wave circuit of 3 phase system and inverter circuit used in ups