Wat wil happen if Transformer is operated at 100 HZ
Frequency?
Answers were Sorted based on User's Feedback
Answer / parimi.venkateswarlu
voltage in winding increase double,due to this effect flux
density increases to doubleit causs high no load losses and
may cause to distroy the core
| Is This Answer Correct ? | 22 Yes | 4 No |
Answer / sendhil
emf e=4.44BAfn volts
if the frequency is increased induced emf also increased so
the induced emf damages the insulation of the winding it
will leads to short ckt
| Is This Answer Correct ? | 18 Yes | 4 No |
as per EMF equation of the trasformer frequency is directly
proportional to winding voltage. if we double the frequency
the sinusoidal root mean winf=ding voltage also doubled.
E=4.44 * f*b*n*a*b
| Is This Answer Correct ? | 21 Yes | 9 No |
Answer / phkhatri
Follwing series of action will occur when 100Hz power is
applied to 50Hz transformer.
1) Core gets saturated
2) No,load losses increases and Temp. too goes up
3) Output voltage cannot be predicted as the core is
totally saturated.
4) Heating continous and gradually damages the core
5) This is followed by heating up of the oil and thus
cooling temperature goes down sharply.
| Is This Answer Correct ? | 15 Yes | 5 No |
Answer / r jp hansalkar
thye transformer iron losses will increase 4times as iron
losses is a function of the square of the frequency.As a
result of increased Iron losses temperature will shoot up.
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / prabal gohain
when frequency increases , Humming sound of transformer increases becz magnetic core has to magnetise and demagnetize at a rate double of its frequency. voltage is the amplitude of the sinusoidal wave(AC),so will not vary with frequency
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.kossay
if we operate the transformer at 100 hz the magnetic flux
inside the core will decrease sharply making the output
voltage decrease
| Is This Answer Correct ? | 12 Yes | 23 No |
What are the necessary solutions needed to be carried out on a malfunctioned earthing mechanism of a VACUUM CIRCUIT BREAKER.(TAMCO)
how to calulate multiplying factor if meter ratio is /5 ampere and ct ratio is 100/5 ampere.(our supply is 3 phase 415 volts)what is multiply factor?
How we calculate DC inducation moter Amp? Sir pls give me formula......
Why you are switching off arc protection mcb when you are taking shutdown for lv board.
a 25kvar capacitor bank connected to the secondary side of transformer.then why the capacitor draws more current then rated
How to calcualte the total number of cells required for particular UPS of some X KVA with 3 and 5 hours back-up?
what is the current law ?
What is the fundamental cause of transients in power system?
In a power conditoining unit (inverter) of a solar plant when we measure the d.c. current fed by different strings of solar plates to inverter, the current in the negative wire is less almost by 1 ampere to the current in its positive wire say current in positive wire 5 A , then current in negative wire of the same string is 4 A. Since the current entering should be equal to current leaving then why the current is noticably less in negative wire.
What is ignition module of a CAT Gas Genset G-3508 Engine, Alternator SR4B Series. HOw its checked for correct functioning.Is it repiarable or replacable?
Ns=120f/p. what is 120?
10 Answers IAR, L&T, Ramada, Toshiba,
What is MS-EXCELL?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)