3.7 kw motor ,how much sq mm cabel want to bare this motor load
Answer / gopal
In case of copper cable 2.5 sqmm is enough. For aluminum 4sqmm is better. Since full load current of 3.7kw motor is 6.4A.
Is This Answer Correct ? | 5 Yes | 0 No |