HOW TO CALCULATE GROUND FAULT CURRENT IN 430V 4000AMP AIR
CIRCUIT BREAKER?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The line to ground voltage is about 250 V , The maximum
ground fault current is, when the phase wire touches the
earthed metal surface and it will be about 250 A ,taking ER
as 0.5 X 2 ohm ,ignoring impedance of the tr.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / wareagle
Not enough information to answer the question.
Need source impedance and KVa rating.
Is This Answer Correct ? | 1 Yes | 2 No |
what is the diffrance between earthing and grounding...?
How we calculat the NGR of 3phase Generator, Our generation voltage 11KV
What is the typical power circuit configuration of a VVVF Drive ?
how to design step down 12 V, 1mA small transformer from 220 V AC? Because according to VI relation and power transfer it results bulky...
What will happen if the voltage in my house drops from 220V to any lower voltage?
What is the reactive power and how to control the reactive power in power plant
what is form factor.and rms value..
Dear sir, we are getting voltage fluctuations suddenly for 2 or 3 minutes again it becomes normal. we checked each and every connection some times we are getting 110 volts like that from earth to neutral again it is reducing we are getting supply from 45 kva DG set give earthing properly.
What is the IS standard for MCCB to be use (As per capacity of AMP)& for ACB also.
HOW WE KNOW IN PHYSICALLY THE CONTACT SURFACE OF A VACUUM INTERRUPTER IS GOOD OR GOING TO DAMAGE IN A VCB AFTER ABOVE 500 TIMES OPERATED.
While DG is on Load? we can start the capacitor bank?
what is the difference between earth and neutral?
56 Answers Bhel, Emerson, HCL, JLL, L&T, Siemens, TVS,