what role does a star point or neutral point play in a star
connected system?
Answers were Sorted based on User's Feedback
Answer / subhendu
1.eliminate 3rd harmonics
2.eliminate voltage unbalanced partially.
3.used in 1 phase distribution system
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / marsad
In a transmission system star connected transformers are preferred than delta connection.. .
Usually the star point is earthed and connected a neutral current transformer in series with the neutral point and ground.. and works as a 3 phase 3 Wire system..
Whenever an internal fault occurs an unbalaced current Flows through the neutral point and then through NCT if the neutral current above a limiting value a relay connected from NCT (called restricted earth fault relay) will actuate.. Which will trip the transformer and protects it.. This can only be done in star connected transformers..
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gravityguru
it provides a point to create potential difference...
between R-N, Y-N. B-N phases....this is in case of 3phase 4
wire system................
hence we can connect balanced or unbalanced load to different
phases
| Is This Answer Correct ? | 1 Yes | 3 No |
why dc source used for HV breakers and Relays operation?
GIVE CONDITION FOR MAX EFFICIENCY OF 3-PH TRANSFORMER AND D.C MOTOR
What is mean by single phasing used in distribution of electricity in rural area of maharashtra state?
sir what is the minimum IR value of 11 KV alternator?
What will happen if the oil level in the buchholz realy of a transformer gets down?
What is the GI Earth Flat Size recomended for 33KV 2000KVA Distribution Transformer
To avoid arcing what we connect in earthing.
Why Ferranti effect not occurs at full load?
Natural frequency in the control system represents nature of a. Transient response b. Oscillations c. Overshoot d. Speed of responce
1)which height building required lightning arrester? 2)how to calculate the requirement of lightning arrester? 3)what is the pro instrument? 5)how to test protective relay like overload?earth fault relay?
if we have 320KVA Genset kindly advice how much load we can put it.
What is the difference between solid grounding and impedance grounding?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)