In power point wiring,often,we use less size of earth wire
compared to phase & neutral wire and we use big size pin in
pug top. how is it justified? can we use small size cable
for earthing?
Answers were Sorted based on User's Feedback
Answer / santosh kawade
We use big size pin and socket for power point to reduce
resistance in earth pat and to alway connect earthing first
to equipment before connecting mains and neutal in system.
Using low size cable for earthing in single phase can not
be justified, we have to use same size cable for neutral,
eathing and mains.
In three phase we can use lower size cable for earthing and
neutral.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / j@ru ( sati)
as we know from R =pl\A bigger the size of area lesser the
resistance of conductor...so b using this concept earth pin
provides less resistance to leakage current compared to
other two pin hence leakage current by pass to earth without
damagng appliances..
thats all thank you
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / shanmugam annamalai
The reason of earth point in bigger than that others to
save the equipments from leakage current. It means, the
system will be earthed before connecting to the power
supply. Ultimately, if there is any leakage current, it
would bypassed through earth so equipment will be safe.
Please reply, It you need more clarifications
| Is This Answer Correct ? | 4 Yes | 2 No |
Whats the difference between three phase and single phase?
Why AC loads wont used in DC input supply? and Why DC loads wont used in AC input supply?
Explain RLC circuit?
What is the diffrence (Technical & Construction ) between CBCT & Normal CT?
Why substation battery room is coulered black?
basic differance between electrical and electronic.
What motor is used in ceiling fans and what motor is used in table fan.? why table fan is costlier than ceiling fan?
What is Phase to Phase clearance for 800V System Operating Voltage as per IEC61439
what is the working principle of DC generator ?
a.)Ammeter and Voltmeter read rms value or avg. value ? b.)What are symmetrical and Unsymmetrical faults?
what is servo motor and how to work it.
In sub-station how to find multifactor of panel?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)