why we use REF and Differential Protection in one
transformers?my doubt is both protections are operated in
internal fault only.why we want to use 2 protections?please
clarify.
Answers were Sorted based on User's Feedback
Answer / ramji
The differential protection is used for protecting the
transformer from internal winding fault,internal winding
shorts etc.,.It operates through three sets of CT's
connected in and out of transformer.It may or may not
operate during minor earth faults.REF is used to detect the
earth fault at restricted zone where its protection CT is
connected.It will surely operate during earth fault.But not
in windings short.
Is This Answer Correct ? | 31 Yes | 4 No |
Answer / gunasekaran
both are using for internal fault but differential
protection only sensitive up to 92% winding of the
transformer if any fault occur in balance 8% winding diff is
not operating so we r using REF protection
Is This Answer Correct ? | 11 Yes | 7 No |
Answer / nikhil thakkar
REF and Differential both pritection are for internal zone and SEF for external zone. Actual all protections are voltage/current/power based and they are back to each other. DIFFERENTIAL AND REF both protection is for internal fault i.e trafo winding . differential sense unbalance between both end of trafo. /Gen. . REF sense unbalance caused between NCT and phase CTdue to earth fault abd actual backup for REF is SEF.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ashish
as per my knowledge ref protections hav to be assigned
separately on both sides of traffo it protects 90% of
winding.
it is unit protection and its very sensitive.
while talking about diff protection two cts in each phase
on both sides of trafo is there any diff in incoming and
outgoing current will leads to trip so both are equally
required.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / raveendra nath
Differential protection provides excellent protection for
phase- to-phase and most phase - to - earth faults, this
element is less sensitive for single- phase-to-earth faults
close to the earth point in solidly earthed transformers.
For these faults (i.e fault at transformer winding turns
nearer to neutral point ), phase current changes very
little, but large current flows in the neutral.
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / gunasekaran
at internal earth fault condition diffrentional sensitive
only 85% only remaining 15% covered by REF protection
Is This Answer Correct ? | 1 Yes | 8 No |
Answer / munish
REF 64T is used for protect the 95% winding of T/F.it sens
only the internal fault of T/F and 51NT circulating earth
fault relay used for detect the other area.
87T diff. is act only when the difference B/W both side
current is more than setting value
Is This Answer Correct ? | 0 Yes | 8 No |
How to calculate the voltage drop of 4 Core 50 Sqmm SWA cable for a distance of 350 mtrs and what can be the maximum load connected to it?
what is the difference b/c choke and ballast?
what is the main parts of transformer? how it is functioning? pls giv the ans briefly.
why wave traps are placed only at y and r phase?
Brushes are placed at magnetically neutral axis,when brushes reach that point,the armature conductor gets shorted,but it can be seen that the dc supply is also shorted,wont that get damage? help me plz
Why birds seating in HT line does not get shock? If person hangs in HT line (single hand or both hands) does he get shock?
WHAT IS THE DIFFERENCE BETWEEN GENERAL INVERTER AND SOLOR INVERTER TELL ME PLZ
tell me the operation of ELCB. How it detects a fault?
What is pi controller?
we all know that in transformer, voltage and current are inversely related i.e. Vp/Vs= Is/Ip....so in standard CT..we have a ratio of 200/5...that means our voltage should increase by ratio of 40..althoug that is not the case...because that requires high insulation level.and pratically not feasible......can anybody clarify my ques.......thanx
What is the acessaries distribution transformer ?
state working of halogen lamp?