during parallel operation of two ac generator which
condition must match before taking both parallel i.e
speed /voltage rating /kva/exciation
Answers were Sorted based on User's Feedback
Answer / pswin
Parallel operation of alternators is called synchronization. A synchroscope is an instrument for indicating the correct time for switching on. Three conditions must be fulfilled for synchronization.
1. Voltage must be same.
2.frequency must be same. And
3.voltage should be in phase position with respect to local series circuit.
Additional requirement is that the phase rotation must be the same.
Is This Answer Correct ? | 27 Yes | 3 No |
Answer / kamlesh g patel
incoming machine voltage should match the system/other
generator voltage.
frequency must be the same.
phase sequence must be the same.
Is This Answer Correct ? | 12 Yes | 4 No |
What is AVR? Explain the function AVR?
Can you any one explain application of buccholz relay operation and pressure relif device operation of power transformer
Difference between on line capacitor and Station type capacitor
What is BUCKBOOST TRANSFORMER and Operation of Buckboost transformer?
How to generate neutral in DG set?
want to know about DMRC
A separately excited dc motor having 2 ohm armature resistsance draws a current of 10A and torque developed is 20 Nm under rated field condtion. the speed of the motor under the rated field condtion , when it is connected to a 100V DC source and delivering 10Nm torque....
What will be the effect if I use inverter as UPS mood?
Good day everyone,currently in our premise we using 30kw slip ring motor with resistance bank which we use as forward and reverse at conveyor bar handling. So,my question is how do we calculate the resistance bank which is suit the motor. Kindly,assist me... thank you
How to select AC3 duty contactor for DOL & Star-Delta starters
why delta delta connection generally not use in transformer
how to calculate full load current of transformer & induction moter ?