In three pin socket normally three pin in between three
pins earthing point is more thickness why?
Answers were Sorted based on User's Feedback
Answer / a.rafeeq raja
As Leakage current need to flow through the Earth Wire
the resisitance should be as low compared to that of the
phase and neutral wires.Besides,The resistance of the
conductor is inversely proportional to the cross sectional
area of the conductor .Hence bigger cross sectonal area
reduces the resistance and provides a easy path for the
current flow.So the Earth Pin is always bigger than the
other two pins in a 3pin plug.
Is This Answer Correct ? | 27 Yes | 4 No |
Answer / rakesh
as we know that R=p*l/a
resistance of the
conductor is inversely proportional to the cross sectional
area of the conductor .Hence bigger cross sectonal area
reduces the resistance and provides a easy path for the
current flow.So the Earth Pin is always bigger than the
other two pins in a 3pin plug.
Is This Answer Correct ? | 15 Yes | 2 No |
Answer / m.srinivas manoj
when a fault occurs a large amount of current is drawn from
earth wire hence more thickness is required to avoid
insulation breakdown
Is This Answer Correct ? | 13 Yes | 5 No |
Answer / ranjith
bigger dia of the pin gives larger contact area with socket
clips which is requard to handle falt corrent. heigher
length is to ensure first contact and last brack while
incerting or removing the plug from the socket.the height
diferance is ensured is the socket std by meens of H dim.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / prashant
when ever we talk about fault current. it always means a heavy current. fault current always needs a path to be grounded. since it is large so it obviously needs conductor having low resistance. since if resistance is high then on passing current through it will produce heat by formula (I^2R). again by seeing formula of resistance
R=P*l/a
increasing the area will reduce the resistance and hence reducing heat energy.
that is why earth wire is kept thick...
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / rk hari
the pin gives larger contact area with socket clips which is requard to handle falt corrent.so the socket std by meens of H dim..
Is This Answer Correct ? | 1 Yes | 0 No |
Which is stiffer between salient pole rotor and cylindrical rotor synchronous machines? Justify your answer.
what is the function of a starter in a motor? explain RLC circuit.
Define cuttoff frequency?
Can any body describe me why a soft starter is used for 6.6kv induction motor instead of VFD ?
How to do the meggering for a cable.
What is your acheivements
3- What is the target from Zero Impedance, Single Phase Imp., S/C Imp. and magnetic balance tests?
If breaker is undefined position, first step to do.
TCS IS IT COMPANY THEN WHY DO THEY NEED ELECTRICAL &ELECTRONICS ENGINEERS?
what is transient earth voltage
Determine the minimum cable size for a 28A single phase final sub circuit originating from the distribution board supplied by three phase submain. The route length of the final sub circuit is 54 m. Assume 1% voltage drop in the consumer's mains. Submain specification: Cable: 50mm2 4 core V75 copper; Route length 42m; Maximum demand 135A per phase
what is wore of PLC ?