What happens when reactive power enters a system?
Answers were Sorted based on User's Feedback
Answer / tareq harb
I did not get ur idea here but i will answer generally:
When reactive power consumption (inductive loads) increases
the power factor go down, current increases in the system,
voltage will drop in transmission cables and generators
terminals & the wasted unuseful energy will increase as
will.
To over come this problem there are two ways:
- installing capacitors in the load side so this capacitors
could supply the reactive power demanded by the load. the
main disadvantage is output energy from the capacitor
depends on the line voltage in case it drops the VARs
supplied will come down.
capacitor place & value should be carefully choosen to
avoid leading power factor if the capacitors supply more
VARs than the load demand.
- static VAR generatos & compensators will produce VARs
nevertheless line voltage but it is very expensive.
the question why the capacitor installed on the load side??
BCZ reactive power dissipation is very high in transsmition
lines so if u put capacitor in generation side u need to
supply huge amountof reactive power to sully small
inductive loads more over the transmission lines will be
over loaded & over heated as well.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / gopal manda
when reactive power is input in a device, then power factor
will be change.because reactive power is two type,inductive
reactive power,capacitive reactive power.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / subhrendu nath
Reactive power is unused power,when it enters the system it
damages the system and develop harmonics.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / vinod
reactive power developing when electrical energy is
coverting another energy through flux, reactive power is
more current will be more for the same active power so we
canot utalise capacity of the generator, t/f, cable etc
| Is This Answer Correct ? | 0 Yes | 1 No |
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer?
Differentiate AC and Dc resistance
i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star connection at both side.but it have another thied winding tertiary winding.what is used of this winding. pl tell me
how to calculate the MF in meter reading
How the size of transformer decreases if we increases the frequency?
help!!!! i bought a new house 2 yrs ago,ive just had 2 new lights fitted,when i boil the kettle,maybe 2 times in succession the safety light switch trips out,it dosnt do it straight away but it seems to do it when the kettle boils!!!!! sounds very odd to me
what is the differation bewreen kwh & fundamental kwh in electronic trivector meters
Why in India distribution transformer are connected in Dyn11 when we know capacity of v-v connection can be increased by adding only a single transformer?
what is the difference between LPF and UPF wattmeter and where it is used.
When in a large power system if the demand of power is larger than the generated power the frequency of the power system drops.(assume the rated frequency is 50Hz and now it is 49Hz) So does this mean the demand is totally supplied with a lower value of generated power in a lower frequency?
why we can't use more then 50 hz in india ? Is it possible ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)