what will hapen if secodery circuit is open of current
transformer
WHy neutral to ground trips when neutral touches the ground
Answer / thowsif_emerson_csm team
The CT Will Burn....
Why does opening a CT's secondary cause dangerously high
secondary voltage?
With the flow of both primary and secondary currents the
transformer's exciting current is very low. The secondary
current mmf serves to keep the magnetizing flux in check!
If the secondary now opens the primary current mmf produces
an exciting current 'orders of magnitude' greater than
normal. And, the resultant large increase in flux density
produces an extremely high voltage in the secondary.
Regards,
Thowsif.
Is This Answer Correct ? | 7 Yes | 1 No |
What is real time power factor control panel(RTPFC)?
when we have to purchase the transformer by own i.e how much load will preferred HT connection?
What are the minimum acceptable insulation resistances of insulation of underground cable suitable for 0.440kV,11kV, 33kV and 66kV?
how does capacitor oppose sudden chane in voltage? how does inductor oppose sudden change in current?
4 Answers AAA, Iqra University,
what is the power ratio between power in star and delta circuit?
why electric shock due to dc is dangerous than that of ac
how to stop oil leakage in power transformer.
is there any chance to get shock from the transformer oil at the time of maintenance due to its dielectric property. . ?
Which device of PlC does share load between DG sets when DG are running in perallel?
What is differnce b/w tie breaker and bus coupler?
in transmission line, if the load is suddenly increased at the receiving end of the system the phase shift will (a)decrease (b)becomems zero (c)increase (d)not be affected
how we calculate the knee point of a protection and metering CT and what is the testing procedure.