how does the switching of capacitors in a capacitor bank
take place when we use them at the load side to reduce the
power factor?
Answers were Sorted based on User's Feedback
Answer / mpn
Switching is done by closing the apropriate contactor in
the circuit. Suppose you have a 30 KVAR capacitor bank, a
40 KVAR capacitor bank and a 50 KVAR capacitor bank. Each
will have a contactor in the circuit. If you want only the
30 KVAR capacitor bank in the circuit, you close only that
paricular contactor. If you want 90 KVAR, you close the
contactor for 40 KVAR and 50 KVAR banks.
Also, please note that there is a mistake in your question.
Nobody will use capacitor bank for reducing the pf. It is
used for improving the pf.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / karthikeyan
by using automatic power factor controller it can be
acheived.
Is This Answer Correct ? | 1 Yes | 3 No |
Why we use the D-curve MCBs in critical power distrubution.
How much Fault current can be contributed by a motor?
which winding aply in an alternator?
How can we convert dc to equivalent ac??
What are the advantages of star-delta starter with induction motor?
7 Answers Merchant Navy, Naval Academy, Samundra Institute of Maritime Studies, YMCA,
What do you understand by external characteristics of a d.c. Generator?
What core magnetic balance test of transformer? How to do this test in a three phase Star star (star-LV, star-HV) transformer? How to measure and where to measure?
Why earthing is necessary for any equipment?
suppose MCC (Motor control center)panel work on field the relay on this damage or not work and earth fault occurs in this and no indication in relay panel given below. than MCB trip or not and what effect the panel how find relay will damage or not work.
what is the purpose of vector group in a transformer ? if 2 tranaformers r connected in parallel the vector group is same or not? for parallel operation 2 transformers of different manufacturers maintain same vector group or not?
Hello Can I use step up HV transformer 440/4160V as a step down? Thanks Evgeny
effect of single phase transformer on full load current?