On a transformer name plate %IZ(%Impedence) is mentioned.
What is the meaning of %IZ and how it is calculated?
Answers were Sorted based on User's Feedback
Answer / bhaskar goswami
Calculating the Short Circuit Current when there is a Transformer in the circuit. Every transformer has “ %” impedance value stamped on the nameplate. Why is it stamped? It is stamped because it is a tested value after the transformer has been manufactured. The test is as follows: A voltmeter is connected to the primary of the transformer and the secondary 3-Phase windings are bolted together with an ampere meter to read the value
of current flowing in the 3-Phase bolted fault on the secondary. The voltage is brought up in steps until the secondary full load current is reached on the ampere meter connected on the transformer secondary.
So what does this mean for a 1000KVA 13.8KV – 480Y/277V.
First you will need to know the transformer Full Load Amps
Full Load Ampere = KVA / 1.73 x L-L KV
FLA = 1000 / 1.732 x 0.48
FLA = 1,202.85
The 1000KVA 480V secondary full load ampere is 1,202A.
When the secondary ampere meter reads 1,202A and the primary Voltage Meter reads 793.5V. The percent of impedance value is 793.5 / 13800 = 0.0575. Therefore;
% Z = 0.0575 x 100 = 5.75%
Taken From:
Simple Methods for Calculating Short Circuit Current
Without a Computer
By Dennis McKeown, PE
GE Senior System Application Engineer
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
full load currentximpedance /rated voltage in %
Is This Answer Correct ? | 5 Yes | 3 No |
why generaters need four earthings
how we provide neutral earth on synchronising panel as per electrical standards?
What is Automatic Voltage regulator(AVR)?
Is motorized MCCB required rotatory handle
what do u mean by bus bar?
Type of cable insulation?
Is a DC Transformer Possible? if Yes, Then Why, if not Then Why?
what is the difference b/c choke and ballast?
What is formula of capacitor for 1-phase power connection.how to improve PF. Suppose I want to connect capacitor in refrigerator to reduce power consumptions.
what are the various parts of airconditioning system used in train and its working
what is V=4.44FBN, THIS 4.44 ONLY U GOT the voltage in term sof 11, 22 etc this 4.44 u will get from form factor which has a value of 1.11
what is principle of DG