Answer / rajkumar
Thermocouple
Type Useful/General
Application Range Notes
B 1370-1700°C
(2500-3100°F) Easily contaminated, require protection.
C* 1650-2315°C
(3000-4200°F) No oxidation resistance. Vacuum, hydrogen or
inert atmospheres.
E** 95-900°C
(200-1650°F) Highest output of base metal thermocouples.
Not subject to corrosion at cryogenic temperatures.
J 95-760°C
(200-1400°F) Reducing atmosphere recommended. Iron leg
subject to oxidation at elevated temperatures--use larger
gauge to compensate.
K** 95-1260°C
(200-2300°F) Well suited for oxidizing atmospheres.
N 650-1260°C
(1200-2300°F) For general use, better resistance to
oxidation and sulfur than Type K.
R 870-1450°C
(1600-2640°F) Oxidizing atmosphere recommended. Easily
contaminated, require protection.
S 980-1450°C
(1800-2640°F) Laboratory standard, highly reproducible.
Easily contaminated, require protection.
T** -200-350°C
(-330-660°F) Most stable at cryogenic temperatures ranges.
Excellent in oxidizing and reducing atmospheres within
temperature range.
RTD Resistance Wire Comparisons
Element Metal Temperature Range Benefits Base
Resistance TCR (Ω/Ω/°C)
Platinum -260 to 850°C
(-436 to 1562°F) Best stability, good linearity 100 Ω at
0°C 0.00385 (DIN-IEC-761), 0.003916 (JIS 1604-1981)
Copper -100 to 260°C
(-148 to 500°F) Best linearity 10 Ω at 25°C 0.00427
Nickel -100 to 260°C
(-148 to 500°F) Low cost, High Sensitivity 120 Ω at 0° C
0.00672
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / ulaganathan
generall for the measurement of low temperature
range is by using thermistor
and for higher order terms i.e>1300 c we are in
use of thermocouple
greater than that temperature we are in use of
pyrometers
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / prashanth
hello Mr.Rajkumar thanks alot for ur reply but the text
alignment seems to be very confusing so if u could just
paste the link for that ans over here it would be very useful.
thanks again :)
| Is This Answer Correct ? | 0 Yes | 0 No |
How to check vortex flow meter is in good condition while we do not having calibration setup?
how to calibrate pressure gauge(we can not able to fixed by pointer screw adjustment and pointer re fixing method)
should I use Hydrostatic Pressure Transmitter for measurement of DENSITY of filled tank ? If YES then please explain how.
difference between vaccum and draft
what is positive feedback and negative feedback?
Explain why use mmwc unit?
Different between control valve and mov
What is difference between ESD and PLC please Explain me clearly.
How u will setup SPI(2007) on Citrix Server (Thin Client Mode)? Plz Justify?
what is the meaning of potential free contact. difference between dry and wet contact?
What is hook's law
which instrument is used to study the structure of phloem and xylem tissue?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)