What type of isolation transformer used in UPS's??
It's Star-Delata Or Delata-Star????Why it is used????
Answers were Sorted based on User's Feedback
Answer / sam
its Delta and star only
to provide electrical isolation
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ravi
IT IS DELTA-STAR ONLY.
TO PROVIDE SINGLE PHASE POWER SUPPLY i.e PHASE TO NETURAL
CONNECTION IT IS USED AS A DELTA-STAR TRANSFORMER.
Is This Answer Correct ? | 11 Yes | 9 No |
Answer / mms
UPS OUTPUT FROM IGBT IS WITHOUT NUETRAL IT IS JUST PHASE
AND CUSTOMER REQUIRED PHASE AND NUTRAL FOR LOAD SO IN UPS
USE STAR OUT PUT TO THE LOAD HENCE THE USE "DELTA STAR"
TRANSFORMER USED IN UPS
FOR EXAMPLE IN SINGLE PHASE UPS OUTPUT(230VAC) WITHOUT
CONNECTING THE DEDICATED EARTH THIS TWO TERMINAL HAS OUTPUT
VOLTAGE FOUND 115 AND 115 VOLTS AND ALSO BOTH POINT TESTER
IS GLOWS THUS WE CONNECT THE EARTHING TO UPS
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / biswajit sahoo
deltastar, beacause neutral is dedicated for ups only. its
neutra is not mixing with raw power neutral
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / hussein
Delta-Star
reason: isolation transformer is to isolate the neutral.
However, the transformer input will be only 3 core cable
(RYB phases) which will be connected as delta, output will
be 4 cores (3 phases and one neutral) and clean earth which
will be commoned to neutral at the star point.
Is This Answer Correct ? | 1 Yes | 1 No |
is there any chart showing the suitable cable size according to AMP and length ? for three phase motors
What are the basic elements used for modeling mechanical rotational system?
State the formula for overall efficiency of thermal power station
why ct output is in 5A?
No load efficiency of transformer is ___________ than full load efficiency
I want formula to calculate cable size as per load given in length & amp. I searched many sites but didn't right answer. Please reply me asap.
IF ANY MATERIAL AVAILABLE IN MARKET FOR MOTOR PROTECTION INSTEAD OF OLR & CONTACTOR ?
why does the magnetic balance tests at transformer?
How to test Power Transfomer vector group in the field?
How does the slip regulator works as a startor
In a 11KV 3phase system do you need to earth both sides of the cable?
I have 380.KVA DG set how to Calculate the units from DG.
2 Answers Ozone Pharma, Sperry Plast Limited, Sterling,