Answer / denzel101
it is a relay that checks for current balance between the
primary and the secondary side of a transformer.it is also
used in other components of the power system like to
protect cables.it is also known as a unit protection as it
does not discriminate with any other protection schemes.the
ct secondary currents that circulates in the coil of this
relay from primary and secondary of the transformer
cancells each other when the system is healthy.when the
fault occurs in a system the balance is disturbed and the
resultant current activate the relay and cause trip.
| Is This Answer Correct ? | 73 Yes | 10 No |
Answer / manikandan
actually differential relay function in transformer . this
relay monitoring the both side current(primary and seconday)
if current diffrent occure in transformer i t will be trip
the incoming breaker.
| Is This Answer Correct ? | 42 Yes | 1 No |
Answer / debajit ghosh
The differential relay calculate the current of primary
side and secondery side within the ratio.
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / charu manchanda
a differential relay is a protective element which finds the
fault or difference between the primary and secondary current.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / krishnanraman
diff relay generally used for finding the difference in
primary and secondary circuit,the relay connect between the
primary and secondary circuit,normally the current flows
through the primary and through secondary thst time relay
is inoperative mode,when fault occurs the primary changes
as per secondary changed thus relay energise and trip the
circuit
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / karthick pdcs
The differential relay which using to check current flow direction.
| Is This Answer Correct ? | 1 Yes | 2 No |
The differential relay which funtion on failure of the
internal phase and earth fault winding insulation damege
ect.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / gopi
1.buhoolez relay.
2.over current relay.
3.earth leakage relay
4. thermal relay
| Is This Answer Correct ? | 20 Yes | 48 No |
why do we earth the tandelta point of a power transformer bushing?
can we coorect P.F. OF 320 KVA ALTERNATOR AT LOCAL SITE WITH RATED .8 PF LAGGING.
What is mean 2XWY
What is the comparison between 30mA DP RCCB and 100mA DP RCCB and can replace it against 63A MCB
WHAT IS DGA TEST FOR THE TRANSFORMERS.
How can w select the cable size for different rating load & also waht r factors affecting the during selection of cable?
11 Answers AB Inc, Bosch, BRB Cable, Lucas TVS, Trisome Technical Services,
Is the installation of the filter cloths necessary before spreading the gravels at the transformer yards?
Load 380kva eb 415v,load amps 350.Same load dg 415v,load amps 420 what reason ?
1 Answers AVT Natural Products,
which motors are used in electric traction?
In vapour absorption refrigeration machine fluids used are
in trains i have seen the terminal which is connected at the top of the train is positive .where is negative ? track? i dont think so
what is our body resistance value?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)