what is diffrent of RCCB & MCCB
Answers were Sorted based on User's Feedback
Answer / hardik vyas
RCCB is Reverse Current Circuit Breaker which gives
protection against earth faults and leakages and is
basically to save people from electric shock.
MCCB is moulded Case Circuit Breaker which is used for
medium current range circuit breaking and gives protection
to system(equipment) against high current and short circuit.
Is This Answer Correct ? | 30 Yes | 4 No |
Answer / annu singh
RESIDUAL CURRENT CIRCUIT BREAKER(RCCB) USED FOR PROTECTION
AGAINST EARTH FAULT . IT CONTAINS CORE BALANCE CURRENT
TRANSFORMER WHICH DETECTS EARTH LEAKAGE CURRENT.
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / murugesan
RCCB detect the leakage current and used for earth fault
and over current also, MCCB moulded case circuit breaker
only detect over current.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / hardik vyas
Hey Saleem....RCCB will not work as a MCCB as it's current
carrying capacity is low.
Is This Answer Correct ? | 9 Yes | 5 No |
Answer / guest
Residual current circuit breaker trips or give protction
against minor fault or leakage than MCCB.
Is This Answer Correct ? | 12 Yes | 9 No |
Where is the center of magnetic field in alternator
Insulater disk using formula for 33/66/135 line h t line
1 Answers Hofincons, Kirloskar, KPTCL,
How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set required to cater to this load?
3 Answers Bhel, INDUS, Indus Towers,
Why transformer making noise during the operation?
what are the different sizes of U.G. cable & where these cabl;es are used according to voltage ..
can i used 400A SFU (for the use of PA fan motor),if my BUSBAR rating is only 315A?????answer me quickly as possible.......thanks
I have 1500/1A CT If i connect this CT in 6.6KV bus bar means what will be the voltage present in CT?
why it is not advisable to run low rating (19KVA) DG sets in parallel for long durations even though they are provided with droop ckts (QDC)
Why Phase to Neutral get spark
Maintenance of transformer???
with the help of drive can we run the 50hz motor on 100hz,what will be its effect.
Does dry and oil transformers both require dedicated neutral, because in my project we are using 2500kv dry star delta transformer, where they say neutral not required and even it is not provided in our substation. can u let me know