How to select power cable for machine
Answers were Sorted based on User's Feedback
Answer / v.senthilkumar - skpcl
According to current rating and Voltage rating.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / sriny(sit)
"The basic thing in selection of cable is depends upon the
current rating of the machine first we have to deside
properly then we go through the selection of cable"
main thing is
1sqmm copper cable takes 7A current
1sqmm aluminium cable takes 3.5A current
Ex : 14 amps motor 2sqmm copper cable but we actually
selected 4.5sqmm copper cable for high current protection
purpose
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / leonid
http://miroshko.kiev.ua/cablesel/wiresel_mini_en - Russian
cable calculator
Is This Answer Correct ? | 2 Yes | 0 No |
What conditions are required for transformer to operate at low frequencies ?
why moisture formation found in XLPE Armoured cable outer sheath
what is the difference between Resin Cast CT and Oil cooled CT?
what is the different types of cable lugs?
2 Answers Green Power, Kum Yang,
why current coil has less number of turns compared to pressure coil?
A TRANSFORMER 440/400V,DELTA/STAR CONNECTED.THE NEUTRAL CONNECTED WITH GROUND CABLE THAT IS DIRECTLY CONNECTED TO THE PANEL,FROM PANEL IT IS CONNECTED EARTH PIT.IS IT RIGHT? IF IT IS RIGHT LEAKAGE CURRENT AFFECTED.SECONDATY IS PROTECTED WITH EARTH LEAKAGE RELAY.
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The slip when motor stalls is A 1 B 0 C 13.33% D 10.33%
In a parallel circuit dc circuit with two resistors, if you know the voltage, amperage, and one resistors ohms, what formula is used to find the second resistors ohms?
in power station what is the electrical circuit length of spacing between power transformer and lightning arrestors,for the voltage system of 230kv,110kv,33kv,22kv,11kv?
1. name the relay for protecting transformer 2. Current Transformer 3. potential Transformer
Which neutral is use when DG(3 Phase)is running?
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer