in 3-phase transformer which type of transformet is used in
output side?
Answers were Sorted based on User's Feedback
Answer / nagaraj n salimani
You mean to say in construction or connection, in connection
type it depends on the application if it distribution
transformer then it will be in Star, and in case of
tranmission it will be delta connected
Is This Answer Correct ? | 15 Yes | 1 No |
Answer / adi
delta-star connection is used for stepping up the voltage to
a high voltage to a high voltage these are used in the
beginning of transmission line so that insulation is
stressed up to 58%of line voltage.....
similarly star delta connection is used for stepping down.
Is This Answer Correct ? | 0 Yes | 0 No |
why do we use star-delta starter. what is its need?
I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila
What is the effect if power factor is above 1 or unity.
Hi, what is 100 % stator earth fault protection and how it can be achieve by 3rd harmonics and low frequency injection principle ?
What are the different auxiliary protections of a transformer?
Why generation voltage in thermal power plant is between 11kv to 33kv?
relation between power station capacity and voltage level?
how we can calculate cable size of 230v,1 hp single phase motor ? panel to motor distance is 25 meter
what transformer we used normally and upto which kva?
what is the function of series reactor
3 Answers Adhunik, INOX, RMSI,
what is dead tank CT AND what is live tank CT
Why we specify TNC switch with 1NO 1NC ,2NO 2NC ? how we get connection.?