if we convert ampers into kwh or mwh ,which one formula use
by us,pls tell me?
Answers were Sorted based on User's Feedback
Answer / omar aziz
Look , Always try to understand what quantities you have
and their significance. This will help you derive other
quantities yourself using the first principles. Lets derive
KWhr from current I !
Firstly you need to know the voltage at which this current
is drawn from its supply. V
Once you have this info you can find the power flow = V x I
this is in W if you use SI units throughout
Divide it by 1000 to get KW
KWh = unit of energy therfore its Power x time
Now how long would your current be drawn for. say its a fan
drawing 2 Amps and you keep it on for 5 hrs at 240V
(240V x 2A x 5hr)/1000 = 2.4 KWhr
Is This Answer Correct ? | 16 Yes | 6 No |
KWH = watt x no of hour /1000
W = v x I for single phase
w = 1.73 x VL x IL x Cos@
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / s.arul
ohms law: V = IR
you know the current rating, you take the machine
resistense using megger. calculate the voltage rating of
machine.
1 phase: power = V * I * power factor (watts)
3 phase: power = 1.732 * V * I * power factor (watts)
ENERGY (KWH) = POWER * TIME
so, we can calculate the KWH or MWH of the machine....
Is This Answer Correct ? | 1 Yes | 0 No |
difference between turns ratio and transformation ratio?
Will MCB tripped off, if there is an electric shock to Human body?
Is an SCR semi controlled device?
What is meant by earthhing of a magnetic flow meter and when to use empty pipe detection?
how we can know which is Lv side and HV side of transformer by just seeing it?
What is Exact meaning for Full load Efficiency and Maximum Efficiency of Transformer? Is there any Difference between? If yes ,please provide with formulae?
why firewall is build up between two transformer (220/11kv,50MVA)?what should be the firewall height?what is the clearance between firewall and transformer?
2 Answers Siemens, Tous Stadt,
can we done C.T.sc at output? if yes y,if no y?
Is there any reason that we get shock on touching phase wire because the earth is at neutral potential? Is there any reason that the earth is at neutral potential because the neutral is earthed in apower station
A 3-phase IM is supplied from 50 Hz system. It runs at speed of 1440 rpm and slip equal to 4 %. Calculate rotor frequency. A 50 Hz B 0 Hz C 4 Hz D 6 Hz
What will happen if the interpoles in case of a generator have opposite polarities to that behind it in the direction of rotation ?
working principle of oil startar