I am getting differential earth fault in my transformer
realy , i have checked all its CT & control wiring but do
not get fault, Please help
Answers were Sorted based on User's Feedback
Answer / jiten sharma
Hi, some times when you charge the transformer after some
duration, trafo will take high inrush current. Due to that
it will trip on overcurrent but some times it can be also
give the triping on differential protection with
overcurrent.
So keep the setting slight high and then charge the
transformer. N after charging keep the setting as it is.
It might solve your problem but before that do the all test
on your trafo and then if nothing will found follow this.
Regards,
Jiten
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / arun
Do all the tests in the transformer windings then you will
get the fault.
Differential protection is given mainly to isolate the
circuit when there is fault inside the transformer.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / engineer
Check all your system(Incuding Cables and trandformer and
control circuit) From 1st CT (at HV Side)to 2nd CT at(LV
side).
| Is This Answer Correct ? | 1 Yes | 0 No |
I think it is REFR which picks up only if there is earth
fault whithin the transformer .i.e. between LT an HT
CTs.and an NCT is to be provided
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Dif relay acts even for faults anywhere between cts .check
cable glands and all others between cts on primary and
secondary
| Is This Answer Correct ? | 1 Yes | 0 No |
10 tube light connect in mcb breaker.one tube light is fault.so breaker is tribe.how fault is rectified.(using 3wire phase,earth,neutral)
what is the difference between brushed alternator ,brushless alternator & permanent alternator ?
How to select the proper VSD to operate high inertial load
cable armor
In electrical what is earth(ground)connection, wht is the importance of it, why it is recomended to maitain below 3VAC between Neutral and earthspecially in PLC used machines?
What is the exact formula for one weber of magnetic flux?
Transmission through a short line depends on
Why transformer rating in kVA not in kW?
what is a motor
How does a digital electronic meter work??????
what happend if we remove dc exciter from moving machine..: gg
In a Capacitor the electric charge is stored in:
2 Answers TELK Transformers And Electricals Kerala Limited,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)