BRIEFELY EXPLAIN MEGGAR PRINCIPLE
Answers were Sorted based on User's Feedback
Answer / khalidshaikh
1.MEGGER WORKS ON THE PRINCIPLE OF OHM;S LAW.
2.FIRST OF ALL IT GENERATES HIGH VOLTAGE THROUGH ITS
GENERATOR OR DC/AC CONVERTOR AND VOLTAGE MULTIPLIER.
3. MORE THE VOLTAGE GENRATED BY GENERATOR MORE ACCURATE THE
RESULTS.
4.IT CALCULATE THE INSULATION RESISTANCE OF THE CIRCUIT
UNDER TEST BY SUPPLYING HIGH VOLTAGE ON THE ENDS.
5. WHEN THE CIRCUIT HAS HIGH INTERNAL RESISTANCE MORE
VOLTAGE DROP AND LESS CURRENT FLOWS AND VICE VERSA.
IT SUPPLIES THE VOLTAGE AT THE RATINGS OF 1 KV, 2 KV, 5 KV
10 KV , 20 KV AND SO ON.
MORE THE VOLTAGE RATING MEGGER WILL BE ABLE TO MEASURE
MILLIONS OF MEGA OHMS AND UP TO INFINITY LEVEL.
Is This Answer Correct ? | 24 Yes | 3 No |
what should be the resistance valve of healthy earth pit
we have 2.2kw,Y,3000rpm motor but 6leads found in TB what happen if we connect in delta?
What difference between TRANSFORMERS and TRANSDUCERS???
what is disadvantages of high power factor
what is allowed value of zero sequence impedancce of 6.6 kv nuetral earthing transformer ?what is the actual value
During the testing of Electrical Equipment the test cables should not touch the equipments. For that testing engineers use to cotton rope to hang the cable from measuring Equipment to testing equipment terminal. Please explain the technical reason for this practice.
What causal system?
why Lightning arrestor are made by 2 seperate stack of inslutor but why cvt are in single stack of insulator.
description with working of all parts of a Diesel generator???????
What are the disadvantages of thermal power plant?
if a damaged 500kva transformer with %impedance 2.6 is replaced by two transformers of 250Kva with different % impedance will they be able to catter the load. what will be the ratio of load on the two transformers if the % impedance is in the ratio 1:2
when 40 watts and 60 watts bulb is connected in series, which bulb glows brightly ?