if we know Fault level say 25 KA , How to decide
busbar size for Distribution network of 1000 Amp
Breaker ?
Sample Calculation or Farmula Available or not ?
Answers were Sorted based on User's Feedback
Answer / bala
2nos.*60mm*1omm copper bar is enough for 1000amps breaker.
formula is available
| Is This Answer Correct ? | 13 Yes | 9 No |
Answer / ritesh m
When current is high then current density become constant.
You can calculate bus bar size by taking current density 1
J=I/S where j is current density, I current & s cross
section.
Then you can calculate size.
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mehul g. c.
if you know the fault level of that area.
then you should find short circuit current.
if you find that then your busbar should be design for that
much short circuit current.
suppose your fault level is 25 ka & then your short circuit
current is 1500 amp. then your busbar should stand safe at
25 ka for 1 or 2 sec until your breaker tripped.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / subrata
125mm X 10mm aluminium busbar is enough for 1000a current (25kA)
| Is This Answer Correct ? | 3 Yes | 2 No |
the fuse is use for protection against overcurrent but at normal condition it carry the rated current then how single thin wire carry this current without melting
where is the need for short circuit test for 3 see is required and why? can you explain in brief with application
For a 500 MVA 400/220/33KV transformer following data given HV power = 500 MVA IV power = 500 MVA LV power = 5 MVA If input power is 500 MVA then how output power is (500+5)MVA. Can anyone help
can we run all LT motors at 360 volts which are normally rated 415+/-10% voltage rating
What is the work of IGBT in ups?
how the harmonics are generated in transforemer?
What is the physical significant of power factor?
Why more than 2.5 MVA distribution transformers (secondary is 440V)are not used in india.
400Kv,can it be generated?why?
New istallation how many eathing have one transformer? Names of earthing connect places?
what is the voltage and ampere rating of all range of HT conductor?
1)we have 1000 cfm Blower,Dia-1Mtr,Velocity of air 94 m/s 2)We have Natural Air velocity 94m/s 3If i Put Wind Mill in natural air ,speed is 94m/s Then it will generate Assume 100kw 4)If i put same wind mill across the Blower,air speed is same 94m/s now the Question is Will it generate 100 kw?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)