Why size of HT cable is less then LT cable inspite of the
fact that voltage is higher in HT cable?
Answers were Sorted based on User's Feedback
size that is the cross sectional area of cable that is in
Sq mm. mainly depends on current carrying capacity of cable
and second on voltage if voltage increases than the
current decreases. so in HT that high tension above 1.1 Kv
current carring capacity decrease for transferring the same
amont of power. so is the size reduced . yes it has extra
insulation for this high voltage.
Is This Answer Correct ? | 37 Yes | 2 No |
Answer / rainy
Hirer the voltage the lower the current. And the lower the
voltage the lower the current. Say for instance if you were
feeding the high side of a transformer with 230kv and the
sec. side was 100kv usually the size of conductors would be
(high side 1 mill. and on the low side would be 2 mill.
wire size usually dual conductors to carry the load on the
low side.
Is This Answer Correct ? | 6 Yes | 14 No |
the power consumption of perminant magnet moving coil?
impliment (AB)`+C to transistor representation
plz explain the snubber circuit unit
Is any AC drive(VFD) had a feature of DC injection braking? if available please mention the detail. i.e drive can supply braking torque when the motor in idle state.
What is sinusodial & non sinsodial current
WHAT HAPPEN WHEN A DROP OF WATER MIXED UP WITH TRANSFORMER OIL ?
at present how many EHVAC lines are there in India?
what will be the magnetizing current in the testing of 27 MVA transformer?
Dears we deal in Chemical are Plate earthing. Kindly call if any requirement and questions. Tech Earth Solutions Mohit Verma 8791071007
Define the overload capacity of the motor?
If you touch power transformer........ Then , in your body current will flow or not...?
why dc is not given to transformer