sorry about the earlier answer.
if the DG or xformers load was balanced when the neutral
failed than there would had been no impact, B cause the
summation current is zero but if it was loaded with a
unbalanced load than the phase voltage would be unbalanced
and cause damage to single phase equipment. the single phase
voltage can raise up to phase to phase voltage depending on
the load current.
| Is This Answer Correct ? | 4 Yes | 0 No |
When do you use a VFD motor?
Kindly Tell me name of the book for electrical estimation and costing ,calculation or web site to download
If one ct is reversely connected in Y system what will effect in kwh and kvarh meter?
Why we are measured insulation resistance applied through DC Voltage?
how to convert kw in to unit
what is the meaning for va and how it is generated
what is difference between MCB & MCCB
Is it necessary to carry out sheath test after cable jointing? If the value is zero of such instance , is it ok to energize the cable?
can i connect wavetrap in 2 different phase in EHV line?
please explain how to do 'pole drop test' on generator?
What is the difference between Relay and Contactor
what is the maximum genarating voltage in india?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)