What is different between Metering CTs and Protection CTs?
Answers were Sorted based on User's Feedback
Answer / ramesh kumar k
Mr. RK is partially right.... I will tell you clearly...
CTs are of 3 types depending on their usage... they are
1. Metering 2.Protection & 3. Special Protection(PS)
Metering & Protection CTs name itself self explanatory.
In metering CTs our main aim is to measure the currents
without damaging the instruments (i.e. Ammeters) connected
to it... so at fault levels (i.e. high currents) the
secondary also indicates corresponding heavy currents... so
the meter connected to it will gets damaged... (A 5A
ameeter can't measure 50A)... inorder to make the meter
safe... we will prepare the core of the meter in such a way
that at faults currents the metering CT core gets
saturated... and it will not induce any more current in the
CT secondary... so the current in secondary ckt. is ZERO.
So the meter is safe... THIS METERING CT WILL BE WORKING
WITHIN NORMAL RANGE OF CURRENT AND WILLNOT WORK IN FAULT
CONDITIONS (IT WILL NOT GIVE OUTPUT).
Where as Protection CT will have to work only in fault
condition. Because the line has to be protected in fault
condition only. The core of this CT is made in reverse to
that of metering CT. It will not saturate in fault
condition and still give the output to the relay...
Thats why Metering CT can't be used for protection
purpose... and protection CT can be used for metering but
it will not meet the accuracy requirements (If accuracy
requiremets are compulsory... prot CT can't be used for
metering)
Where as
Is This Answer Correct ? | 32 Yes | 1 No |
Answer / rk
metering cts are desined not to record fault current i.e.
if ctr is Ex. 200/5 at a fault current of 2000amp the
secondary current would be still 5 amps not 50amp. reverse
is in prot cts it will serve 50amps if its ALF permits .
Metring CT are like acc class 0.5 etc Protn CTs have 5P10,
5P20etc i.e. it will maintain its ratio up to 20times the
the primary current (200amp)of ct.
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / siddharth tayade
mainly the class is diffrence in the protection and
metering c.t.and knee point voltage is conciderd in
protection core
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / asit sarkar
Generally CT have two error 1.Phase angle error,2.Ratio error.
Now,in Metering CT we have to minimize the ratio error as
well as in case of Protection CT we have to reduce the phase
angle error.
Is This Answer Correct ? | 4 Yes | 9 No |
Explain the functioning of diode?
what is the difference between star and delta connection?
What is the calculating formula for HT and LT amps in a transformer.
two 100W/230V bulb are connected in series. what would be the voltage drop across 1 bulb
please explian how may types of maintenance works.
DG Earth Value?
0 Answers Reckitt Benckiser, Vodafone,
what will happen reduce the transformer voltage from 415v to 406v, is it save the energy,? are this methodis good to reduce the energy.?
why neutral and body earthing of transformers kept separated? what is distance between two is required as per is?
what is subtransient , transient and study state ac components
Why two phase welding machine is used instead of three phase welding machine.
what is open star connection or open delta.
Why do we need ring main unit (RMU). what is its purpose and its advantages . what is the operating function of rmu