Answer / ramesh kumar k
Mr. RK is partially right.... I will tell you clearly...
CTs are of 3 types depending on their usage... they are
1. Metering 2.Protection & 3. Special Protection(PS)
Metering & Protection CTs name itself self explanatory.
In metering CTs our main aim is to measure the currents
without damaging the instruments (i.e. Ammeters) connected
to it... so at fault levels (i.e. high currents) the
secondary also indicates corresponding heavy currents... so
the meter connected to it will gets damaged... (A 5A
ameeter can't measure 50A)... inorder to make the meter
safe... we will prepare the core of the meter in such a way
that at faults currents the metering CT core gets
saturated... and it will not induce any more current in the
CT secondary... so the current in secondary ckt. is ZERO.
So the meter is safe... THIS METERING CT WILL BE WORKING
WITHIN NORMAL RANGE OF CURRENT AND WILLNOT WORK IN FAULT
CONDITIONS (IT WILL NOT GIVE OUTPUT).
Where as Protection CT will have to work only in fault
condition. Because the line has to be protected in fault
condition only. The core of this CT is made in reverse to
that of metering CT. It will not saturate in fault
condition and still give the output to the relay...
Thats why Metering CT can't be used for protection
purpose... and protection CT can be used for metering but
it will not meet the accuracy requirements (If accuracy
requiremets are compulsory... prot CT can't be used for
metering)
Where as
| Is This Answer Correct ? | 32 Yes | 1 No |
Answer / rk
metering cts are desined not to record fault current i.e.
if ctr is Ex. 200/5 at a fault current of 2000amp the
secondary current would be still 5 amps not 50amp. reverse
is in prot cts it will serve 50amps if its ALF permits .
Metring CT are like acc class 0.5 etc Protn CTs have 5P10,
5P20etc i.e. it will maintain its ratio up to 20times the
the primary current (200amp)of ct.
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / siddharth tayade
mainly the class is diffrence in the protection and
metering c.t.and knee point voltage is conciderd in
protection core
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / asit sarkar
Generally CT have two error 1.Phase angle error,2.Ratio error.
Now,in Metering CT we have to minimize the ratio error as
well as in case of Protection CT we have to reduce the phase
angle error.
| Is This Answer Correct ? | 4 Yes | 9 No |
How can we reduce the reactive power consumption of your 12.5 MVA power transformer.
What is the Nyquist criterion regarding control systems?
how can testing using megger?
trasnfarmaer core make
at what base you will tell the direction of rotation of dc motors and generators?
Why USe In -48 DC Volt !
Whay you want to change your job.
what is the mager value of star motor and delta motor between phase to ground and phase to phase, and minimum how much should be value ?
what will happen if a cw rotating altenator being synchronized to ccw rotating altenator
What is the advantage of Neutral graunding transformer insted of Neutral graunding Resistance in generating station explain briefly.
why transformer fuse wire is very thin as compared to home fuse wire while voltage lavel is low
how can we change the rotating direction of single phase AC induction motors?
12 Answers Heubach Colour, L&T, MNM Jain Engineering College,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)