how to calculate the size of cable for 100 kva load,?can
somebody tell me with a formula
Answers were Sorted based on User's Feedback
Answer / naresh kumar dhal
100kva load has total current of-139 amps.
if we consider derating factor=0.8
Then total current=139/.8=173 amps
For 173 amps we can use 120 sqmm cable.
Its current capacity=1.5*120=180amps
Is This Answer Correct ? | 33 Yes | 17 No |
Answer / piyush
what is mean of x ?& how to clculat cable sizes 35 -------
sqmm please tel in detail
Is This Answer Correct ? | 18 Yes | 10 No |
Answer / sridhar nayak
P=1.732VI
u calculate i,take voltage 415V for three phase LT
if i=x,than cable size x=20 or 30
cable sizes are-35,75,95,120,150,185,240,300,400sqmm
it apllicable for alluminium cable only
Is This Answer Correct ? | 16 Yes | 15 No |
Answer / kather oli
100 kva 140amps.so, 4core armoude aluminium 100 sqm 4 core
correct cable
Is This Answer Correct ? | 12 Yes | 13 No |
Answer / manoj patel
From KVA , You get value of Amp.
By using standard cable catloge (size versis capacity)
you can find cable size.
That is only way to find cable size.From my point of
view there is no standard formula for that.
Is This Answer Correct ? | 7 Yes | 11 No |
Answer / venkatesh
1kva=1.7amps
100kva=170amps
firstfall we are find out cable item aluminium or copper
aluminium gives 1sqmm=1amp sand copper gives 1sqmm=2amps
but we can use more than 2amps beacuse cable long time will
not come.we have to select aluminium cable for 185sqmm
beacuse total load is 170amps 185sqmm is enoff
Is This Answer Correct ? | 14 Yes | 22 No |
In 1000KVA Transformer why does we connect HT with delta connection and LT with star connection.Illustrate by showing formula?
we the the value of frequency is 50 HZ in DG then why we said the value inductive rectance is zero in DG?
What is SFU why it is used
Can RCD's used to protect the VVVF drive if not why.
how to calculate cable size in diffrent loads?
Single line digram for 11 kV to distribution use go,la and do
WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?
WHAT IS THE REASON OF CHANGE FREQUENCY IN DG SET AFTER FULL LOAD.
for 5KW resistive load can anyone please suggest me whether to go for UPS/Inverter or Generator depending upon cost calulations
what is difference between neutral and ground wire?
What is diference between ELCB & ELMCB?Also how its application for use in design area?
Why are some relay circuts designed to have the ct current flow through the neutral instead of the phase wire, such as in some diff relays?